If the digital VSR is latched in the closed (connected) condition then both batteries will share the discharge.

The common ground must be on the load side of the shunt, not the battery terminal.

Have a read of this about SmartShunt wiring.

> [@Shunt / battery monitor not reading the correct SOC/ Amps, missing solar, decreasing daily or other misreading problems](https://community.victronenergy.com/t/shunt-battery-monitor-not-reading-the-correct-soc-amps-missing-solar-decreasing-daily-or-other-misreading-problems/87):
>
> This topic covers the SOC / Amps reported by BMV battery monitors, SmartShunts, Lynx BMSs and Lynx Shunts and will just be called shunt below. It is also assumed that the shunt is monitoring the domestic / house / cabin battery bank and not engine start / bow thruster / winch / caravan mover battery banks. The problems may be one or more of the following The SOC decreases daily despite the solar charger or other charger(s) working. The SOC increasing when discharging and falling when charging…

---