Do you have any ESS assistants installed and enabled?  
Because in order for what you want to work, according with the scripts, you need to:

1. Have the assistant with ID=5 installed. I suppose it’s the ESS assistant. Check **/Hub4/AssistantId = 5**
2. Have the Multi with the AC connected. Check **/Ac/ActiveIn/Connected = 1**
3. Have DC coupled feed-in excess enabled. Check **/Settings/CGwacs/OvervoltageFeedIn = 1**

If all are checked, then the system will maximize chargers’ production.

---