# Smart Solar MPPT charge controller 150/45 not "ON"

**URL:** <https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011>\
**Category:** Q&A and troubleshooting\
**Tags:** bluesmart\_ip22, victron\_community, diy\
**Created:** [20 November 2025 21:30 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011 "2025-11-20T21:30:18Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [20 November 2025 21:30 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/1 "2025-11-20T21:30:18Z")

</div>

I recently upgraded to a Victron Energy Smart solar mppt 150/45. I have a 320-watt solar panel that is producing over 30 volts open current, which is way over the 5 volts needed to start the charge controller. However, when I hooked the PV to the charge controller and tested the terminals, the voltage goes down to 13.2, the same as the battery side on the charge controller. The Controller is not “ON”. What do you think could be going on. Could it be another bad charge controller?

| ![](https://europe1.discourse-cdn.com/victron/original/3X/d/6/d6a994ae461f14309da5c1b70f72895f6aef91b6.jpeg) | |
| --- | --- |
| | |

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [20 November 2025 21:37 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/2 "2025-11-20T21:37:20Z")

</div>

Hi @Scottyh1960

Did you try to connect the solar charge controller with the Victron Connect App with your Smartphone?

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [20 November 2025 21:37 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/3 "2025-11-20T21:37:43Z")

</div>

Yes

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [20 November 2025 21:39 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/4 "2025-11-20T21:39:56Z")

</div>

And what values did it show about the Solar Panel?

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [20 November 2025 21:40 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/5 "2025-11-20T21:40:07Z")

</div>

In the app the Solar voltage is 13.08 and it says the Batt. is 13.20

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [20 November 2025 21:41 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/6 "2025-11-20T21:41:25Z")

</div>

0.0 amps

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [20 November 2025 21:41 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/7 "2025-11-20T21:41:51Z")

</div>

The solar voltage is too low.

Did you tried to messure it at the Terminals with a DVM?

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [20 November 2025 21:44 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/8 "2025-11-20T21:44:17Z")

</div>

Yes. The open voltage is over 30v (with it disconnected from the Charge Controller)

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [20 November 2025 21:47 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/9 "2025-11-20T21:47:57Z")

</div>

Seams that there is something wrong with there..

Polarity is OK\_

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [20 November 2025 21:50 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/10 "2025-11-20T21:50:24Z")

</div>

I believe so. Red to + Black to -

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [20 November 2025 21:54 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/11 "2025-11-20T21:54:35Z")

</div>

![IMG_0296](https://europe1.discourse-cdn.com/victron/original/3X/e/c/ecaa6916f87e3b8a67bfaf36cee0340f0e1d45ab.png)

Should look like the pic….

Please check the PV voltage at the terminals

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [20 November 2025 22:12 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/12 "2025-11-20T22:12:49Z")

</div>

Mine shows 0 watts. PV voltage on the roof is around 30v. Open current by the controller is around 30v. Its when I put the wires into the Controller that things go bad. Goes down to 13.1v

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [20 November 2025 23:37 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/13 "2025-11-20T23:37:10Z")

</div>

Do you have a laboratory power supply?

Apply 24V, 1A, direct to the pv inputs, for example; the solar controller must work with this.

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [20 November 2025 23:41 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/14 "2025-11-20T23:41:07Z")

</div>

It sounds like a poor connection somewhere in your PV wiring. You test with a multimeter and see 30V, but at that stage it is not pulling any current so poor connection has no effect. Once you connect to the MPPT and it tries to draw current, the voltage at the end of the wires collapses due to the high resistance of the poor connection and voltage drop. A broken panel could also do this. Have you tried a short circuit current measurement if your Multimeter can handle the Isc of the panel.

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [21 November 2025 10:39 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/15 "2025-11-21T10:39:40Z")

</div>

Silly question, but the charger is turned on?

 ![grafik](https://europe1.discourse-cdn.com/victron/original/3X/8/7/8771ad79901478cdeaac8ee0a0ac9d79b84a466a.png)

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [24 November 2025 20:28 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/16 "2025-11-24T20:28:11Z")

</div>

Im not sure HOW to test the panel with my Multimeter.

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [24 November 2025 20:28 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/17 "2025-11-24T20:28:47Z")

</div>

Yes. that is on.

---

<div class="post-metadata">

**Author:** ![Scottyh1960](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/scottyh1960/32/39982_2.png) [@Scottyh1960](https://community.victronenergy.com/u/Scottyh1960)\
**Post date:** [24 November 2025 20:30 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/18 "2025-11-24T20:30:42Z")

</div>

You lost me on that one. Laboratory Power Supply?

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [24 November 2025 22:06 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/19 "2025-11-24T22:06:15Z")

</div>

[![](https://europe1.discourse-cdn.com/victron/original/3X/f/8/f8bbb07b785a01f3bd600a6ab5995ca521cce837.jpeg "How to Test Your Solar Panels Using A Multimeter - Rich Solar Talk") ](https://www.youtube.com/watch?v=WkhLKtsIBeM)

Not easier than that…

---

<div class="post-metadata">

**Author:** ![DirkW](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dirkw/32/33865_2.png) [@DirkW](https://community.victronenergy.com/u/DirkW)\
**Post date:** [24 November 2025 22:08 UTC](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011/20 "2025-11-24T22:08:36Z")

</div>

Something like this

> **[Laboratory power supply - what is it and what is it used for? - Botland](https://botland.store/blog/laboratory-power-supply-what-is-it-and-what-is-it-used-for/)**
>
> Read our article on: Laboratory power supply - what is it and what is it used for? We invite you to read!

[Next page](https://community.victronenergy.com/t/smart-solar-mppt-charge-controller-150-45-not-on/49011.md?page=2)