Smart MPPT 100/20 is not producing

Hello Victron community,

I’ve been trying to solve a problem on my own for quite some time, and I’ve finally come here for help because neither my distributor nor my fellow installers can find a solution.

I’m at an off-grid site with a MultiPlus-II GX, a Smart BMS NG with a Distributor, a Victron 24/100 NG lithium battery, and two Smart MPPTs: a 150/45 for a field of four panels (two in series, with the two strings in parallel) facing west, and a 100/20 with one panel facing east.

The 150/45 is producing really well! However, the 100/20 has never produced any power. It does detect a PV voltage of 36 V, though. If I switch off the 150/45 to give the 100/20 a chance, there’s still no production.

Everything is connected to the VE.Smart network and is detected in VRM. However, I can’t get any production from this unit. I’ve already tried replacing the MPPT to rule out a faulty unit. I’m hesitant to share my VRM here because I haven’t really secured access to the system.

I’m completely out of ideas and really need your help, please… Let me know what information would be useful to help resolve the problem.

Kind regards,

Is the 100/20 switched on as a charger? Have a look in Connect!

In combination with a GX device you don’t need VE.smart network, please disable that.

Can you share some screenshots please?
(Overview page and history)

Can you post some screenshots from Victron connect?

Hello,

The site has gone into winter mode: the system has been switched off.

Here’s what I can share with you for now

Just a silly question from a newbie: have you checked the panel, cable and connector? Maybe there’s a fault before the MPPT, in which case the system would probably detect it. The MPPT doesn’t produce any power itself; it just “manages” the power generated by the panel and passes it on.

Please check that the panel’s positive and negative terminals are connected correctly.

If they’re connected incorrectly, it won’t charge.