Three-phase system with 9 MultiPlus-II 48/15000 units in a three-phase parallel configuration, coupled to an AC generator

Continue the discussion from Validation of the parallel configuration of 9 three-phase Multiplus 15K units (3x3):

In a three-phase system with 9 Multiplus 15K units (3x3) and an external transfer switch, should the AC inputs of the 6 slaves be connected to the incoming AC grid or not?

My question comes from a request for clarification from an important BESS systems client that we support on major projects. We have already sent them the Victron document 1. Introduction

Thanks for helping to clarify this.

In a three-phase system with 9 Multiplus 15K (3x3) and an external transfer switch, should the AC inputs of the 6 slaves be connected to the incoming AC grid or not?

My question comes from a clarification requested by an important BESS systems client that we support on major projects and to whom we have already sent the Victron file 1. Introduction

Read the manual:

Document read previously.

Doubts have arisen, both for me and for my client, with whom I had shared the file, regarding what is stated in point 1 of the document’s introduction.

1.1. Advantages

  • Reduce installation time and costs: This reduces costs and installation time, especially for large systems with multiple MultiPlus(-II) units in parallel. It removes the need to wire each unit’s AC input and output terminals.

We tried to interpret this statement as meaning that the AC-IN references only needed to go to the 3 masters, but we’re not convinced.

The hypothetical diagram we tried to draw, which we’re not convinced by, is this one.

However, we don’t know what the firmware designed for this configuration does with the outputs connected in parallel.

Document read previously.

Doubts have arisen, both for me and my client with whom I had shared the file, regarding what is stated in point 1 of the introduction of the document.

1.1. Advantages

  • Reduce installation time and costs: This reduces costs and installation time, especially for large systems with multiple MultiPlus(-II) units in parallel. It removes the need to wire each unit’s AC input and output terminals.

We tried to interpret this statement as if the AC-IN references only needed to go to the 3 masters, but it doesn’t convince us.

The hypothetical diagram we tried to define, which doesn’t convince us, is this one.

However, we don’t know what the firmware specific to this configuration does with the outputs connected in parallel.

Il punto 5 del manuale però confermerebbe che gli AC-IN degli slave non vanno connessi, e quindi lo schema ipotizzato sarebbe corretto.

Inverter/charger connection Issues

The inverter/chargers fail to connect to the grid or generator:

  • Check whether the AC-In terminals on slave units are wired. They should not be wired.

The link I posted is what you need to read, it says:

For paralleled units, connect only the master unit (of each phase) to the AC-IN terminal and leave the slave units’ AC-IN terminals unconnected.

The ACin on the Master can also be connected using 1.5², as these are used as measurement points.

The main connection is made via the externally controlled relays and ACout. It’s clearly described in the manual!