Maximum conductor cross-section on the contactors of the "Anti Islanding Box"
Hello, does anyone know the maximum conductor cross-section that can be wired into the contactors in the Anti Islanding Box enclosure (with the ZIEHL UFR1001E inside)? There is no documentation for this enclosure … Thanks in advance
12420-0701-32 page 24
Edit: You probably meant the other contacts in the box provided by Victron.
I can’t find any specific info either. probably max 10-16mm2. (wrong, see below edit)
Edit 2: if it’s actually the Legrand DX3 4-pole D63 circuit breaker,
87045 LIMOGES Cedex page 2 :slight_smile:
That’s right, I’m talking about the contactors that are mounted in the enclosure with the Ziehl …
I’d like confirmation of the maximum cross-sectional area.
You can read that from the ABB contactor’s datasheet. It should be 25 mm², but I’d be careful with ferrules, as it always depends on the type of crimp.
Thanks for your reply. I didn’t even know they were ABB contactors. Would you happen to have the part number so I can find the datasheet?
It’s a picture… perhaps you can’t assume that it always comes supplied with an ABB contactor as standard, but I’d argue that I’ve never come across a 63 A contactor where a pair of 10 mm² cables wouldn’t fit.
Perfect, thank you very much!