I run my MP-II 48/3000/35 and Cerbo in ESS3 mode. My Dchouse LFP485002 battery (16 S, 50 Ah) has no data from its BMS, so all I have is the voltage on the outer terminals. Of course I try to make my loop as safe as possible and there is the timeout if all else fails.

Still it would be good to know the MP-II itself limits the charge and discharge before the BMS cuts in. Can someone please explain, where I can find and set the relevant setting and those for the low-bat warning?

Danke
Axel

Yes, the Mp units are given a basic configuration (Ve.Configure, connect), but it’s not ideal if the BMS can’t control the charging current and charging is abruptly shut off (because, for example, you don’t know how the BMS is programmed).

You can also enquire via Where to Buy with a specialist in your area (trained installers, dealers) and ask them to take a look.

Are you wanting to set it (the charge amps) from your control loop?
What are you using to control the inverter?

The low battery warning can come from several places one is of course the inverter tab one when you program with VE config
The other from the dynamic cut off values In the ess assistant

I am controlling it from an external loop and it works. But the low battery warning and alarm on the MP came up when they shouldn’t. It’s probably down to something I set myself. So my question is:

What exactly sets those limits and where?

The next question is: Even with ESS3 in operation, can the MP activate a more conservative safety and shutdown limit than the extremely low discharge at which the BMS cuts in? An external loop can never be as reliable as internal safety settings can.

How did you program the inverter itself? It’s base programming…?

Show your settings here. You can also export them as a .txt file in Ve.Configure.

First, a grateful thanks to both of you for your help. Much of this is quite confusing for me.

As I said, I use ESS3. I write to the "“ESS power setpoint”, slave: 227, address: 37, every six seconds to avoid the very short timeout. How these values are derived is irrelevant here.

The settings are these. They are a first attempt and certainly up to being improved. For quite a few things I’m confused about what they are and what they do:

Model: MultiPlus-II 48/3000/35-32
S/N: HQ2432Z7TJ7
Firmware: 2629508

TAB: General
System frequency 50Hz
Shore current 10.0 A
Overruled by remote checked
Dynamic current limiter unchecked
External current sensor connected (see manual) unchecked
State of charge when Bulk finished 95.0 %
Battery capacity 50 Ah
Charge efficiency 0.95
TAB: Grid
Country / grid code standard Germany: VDE-AR-N 4105:2018-11, internal NS protection
AC input 1 Above selected gridcode plus LOM B (compliant)
rise-in-voltage protection U> 253.0 V
start network service HF treshold 50.20 Hz
P(f>) droop 5.00 %
Use AUX1 as disable FeedIn signal checked
Maximum AC current for charge or feed in 100.0 %
Reactive power regulation Use a fixed Cos Phi
Filter time for reactive power 3.3 s
Cos phi 1.00
TAB: Inverter
PowerAssist unchecked
Inverter output voltage 230 V
Inverter DC shut-down voltage 47.00 V
Inverter DC restart voltage 49.00 V
Low DC alarm level 48.00 V
Do not restart after short-circuit (VDE 2510-2 safety) unchecked
enable AES unchecked
TAB: Charger
Enable charger checked
Weak AC input unchecked
Stop after excessive bulk unchecked
Lithium batteries checked
Disable VSense (for diagnostic purposes) unchecked
Configured for VE.Bus BMS unchecked
Charge curve Fixed
Absorption voltage 56.80 V
Float voltage 54.00 V
Charge current 30 A
Repeated absorption time 1.00 Hr
Repeated absorption interval 7.00 Days
Absorption time 1 Hr
TAB: Virtual switch
TAB: Usage
Virtual switch usage Do not use VS
TAB: Assistants
TAB: Assistant Configuration
ESS (Energy Storage System) (size:1846)
*) System uses LiFePo4 with other type BMS
(This can be either a BMS connected via CAN bus (e.g. a Lynx Smart BMS) or a
BMS system in which the batteries are protected from high/low cell voltages by
external equipment.)
*) The battery capacity of the system is 50 Ah.
*) Sustain voltage 50.00 V.
*) Cut off voltage for a discharge current of:
0.005 C= 51.30 V
0.25 C= 50.50 V
0.7 C= 49.50 V
2 C= 48.00 V
*) Inverting is allowed again when voltage rises 1.50 V above cut-off(0).
*) Restart PV Inverters when the (temperature compensated) battery voltage
becomes lower than 52.50 V.
*) The solar converter will start reducing its output power at 50.20 Hz.
Output power will be reduced to minimum when the frequency is 52.70 Hz.
The converter will disconnect when the frequency is higher than 53.00 Hz.
*) Total installed PV inverter power is 800 Watts.
Total installed PV panel power is 1000 Watts.
*) Relevant VEConfigure settings:

  • Battery capacity 50 Ah.
  • PowerAssist unchecked
  • Lithium batteries checked
  • Dynamic current limiter unchecked
  • Storage mode unchecked

Total size of all assistants including the required
(hidden) system assistants is: 1919
TAB: Advanced
limit internal charger to prioritize other energy sources unchecked

This is where the low battery warnings are coming from.

Check them Vs the c rate discharge (load) and voltage at the time

Thank you. Can you suggest sensible values for a 16S battery? The defaults looked like 15S, which is why I raised them.

Secondly. From the lack of answers I gather that in ESS3-mode no safety fallback against overcharge or overdischarge is provided. My loop is designed for safety but it does rely on external buses. I had hoped for an internal override. No such luck, it seems. Can you confirm?

Danke

No idea.
Are they A grade Cells b or c grade?
Is the battery rated for a 1c discharge and charge rate or less?

For the dynamic cut off just set them all to the 2 c rating for now, see if that clears your low battery alarm.

(Afterwards set it to the 0.25C seems like that is what is recommended from the datasheet it can be the same value as the low cut off you are comfortable with - I don’t think that it will let you go to the 40v it says it will more likely be 47v.)

As for evaluation of what your system is and can do that cannot be done over the internet blind.

Edited:

I stopped being lazy and looked them up.

This is high set it to 25A.

There is a possibility that you are tripping the BMS and the low battery warning are because the battery is unstable.

Set faster values is the answer so it cannot overcharge or discharge, then your loop can override that through DVCC. It will then be safe the the control loop stops working

Best thing would be to watch the information on the app and see how it behaves.
Ultimately there is a tonne of conflicting Information about how lifpo4 should be treated but the BMS and manufacturers of your battery have set their own things there and the battery physically will have its own quirks and that must ultimately be obeyed.