RV battery/inverter troubleshooting after adding MPPTs

Normally a shunt is on the negative bus between the loads and batteries?

Yes, it is but the battery temp sensor runs off the shunt and it is connected to the positive bus bar.

In the meantime, I have another issue, the BMS seems to have gotten confused. Ughh…

Can you still access it with the app? If so, post screenshots

I think I might have it ‘fixed’ but I don’t understand why it’s happening. I’m finding having a computer controlled battery has introduced a variable over the old SLA’s :face_with_spiral_eyes:
And there’s more..

Because the old inverter system could only do 1,500 watts I never saw the cables heat up (stress test). So the other day I was drawing, as it turned out, 350A or so, and eventually the inverter shut off due to heat! :laughing:

I never saw that before so it took a bit to figure out what just happened.

Yesterday, the BMS shut down the battery several times. The draw at one point was 375A - over the 300A rating.

In the meantime, the draw melted that Guest switch we were talking about, so I have a new higher rated one coming tomorrow at which point I will go over every connection and crimp and then the cabling should be OK.

Anyway, to the BMS issue. Logging into it with the Overkill app showed that it had 5 entries for shutting down due to too much draw. So what I did was clear those entries to start fresh. When I did that I noticed something odd, the battery would only charge up to 50% I don’t know why, but it’s repeatable.

I do have it charging 100% now so I think I’m back in business but I suspect that the moral of the story is that the battery is able to outperform the rest of the system so I should keep the draw down to something like 200A. It does make me wonder about the 2/0 cabling and whether it should be 4/0 but then that also makes me think I should have went 24V with a bigger inverter.

I’m trying not to think too much - it’s causing issues :face_with_spiral_eyes:

Update: Cell balance DeltaV is coming into line. With the Multi set to Float (instead of shutting off due to Ignore AC Load) and the float at 13.8 (as previously suggested) the passive balancer remains active continuously. Since it was fully charged (14.2v) it has to work a lot to lower that one cell down.

Understanding this I turned on all the DC lights in the unit to burn off the battery voltage from 14.2v to the 13.8v float - at that point the passive balancer was able to start working very effectively to bring that cell down and balance the pack. DeltaV as it stands right now is .015 which is what that parameter is set to in the BMS. It might be time to lower that a little to get the perfect balance.

You guys probably all know this already, but I found a really great definitive guide to everything Overkill Solar BMS Guide - it’s everything I needed to know.

As you can see, I’m on the way to getting the cells balanced :grinning_face:

In the meantime, I have a dumb question. Since I’ve now seen how warm 2/0 cabling gets under 300A loads, I now understand why making a 24V system is way better. Higher voltage, less amperage, meaning cheaper cables and less loss due to heat. It should be more efficient all the way around.

So for sure, if I was aware of this back in January when I bought the inverter, I would have done that from the start. But here’s the thing, since the DC side of the motorhome is 12V, had I gone to 24V, how do you feed the RV 12V?

I use a 70A DC/DC converter feeding a small 12V battery. The battery is only because we have a hydraulic pump. The 70A because it has nicer connections than the smaller devices. Once the reverse charging on the Orion XS gets sorted out, I’ll be getting one to replace the dumb 70A.

BTW, 24V makes your solar much more efficient too: 30A at 12V vs. 30A at 24V

You’re seeing the large currents because the inverter has to make an output wattage to match your load.

As the voltage drops from smaller wires, the current draw goes up to get the same output wattage, which causes the voltage to drop, which causes larger current draw…

I have a large hydraulic pump as well for the jacks. And there’s two motors for the slide outs…I forget how many watts the jack pump takes but it’s a lot. Same with the slideouts. So it’s not just the lights. There’s probably more that would come to mind but those are the big ones.

Apparently the jack pump is 80A with a startup spike to 100A !

That’s a perfect value when the battery voltage is 14.2V. Setting a lower DeltaV causes other problems. But 14.2V is too high in the long run. It overcharges the cells. You should only do this when balancing is needed. 13.6V is enough.

This is suitable for up to 195A, provided it is installed in free air so it can dissipate the heat.

Compared with 12V, 24V has two advantages: the charge controllers can transfer twice the power, and the cable cross-section can be reduced to a quarter. A 12V system works just as well with modern inverters. Converting 24V to 12V at high currents is problematic. Also, the module voltage must still be high enough when a substring is shaded. That’s a problem too. So 12V is right for you.

Everything is coming together people. I’m so grateful for all your help. I found out that when you change a setting in the KillerSolar app, and write it to the BMS, it screws up the SOC reading. This is why I ran into that issue. The way to fix it is just a complete discharge and recharge - so that’s why it appeared intermittent and so peculiar.

At some point I’m going to get the RS485 communicating with the Cerbo. This battery is incredible, LifePo4 is unreal. In the meantime, I’m getting closer to achieving balance…only a little ways to go!

BTW, I have a new disconnect switch coming as well some new 2/0 and I will just redo the few lugs that are still original. I bet this will address the voltage discrepancy. I also ordered up a Mopeka for either the fuel tank or the propane tank.

OK, back to the original issue which is that the Victron displayed voltage differs from the battery BMS which is dead accurate. Sometimes by .5V or more, I’ve seen it at one point at close to a 1.5V difference IIRC.

Earlier you mentioned testing battery connections, I suspect the idea being resistance should be the proximate cause of the discrepancy.

To that end, I ordered up some new cabling, lugs, and a disconnect switch to address various design issues/clean up as the way forward unfolded.

Point being, most lugs have been replaced but some haven’t so just pull the cables, inspect and replace all the old ones so that I know the connections are solid and then hit them all with the multimeter under load for confirmation.

But, as I plan the job for tomorrow, I realize that the 2/0 positive cable has many connections between the inverter and the battery.

On the positive cable alone we have…

  1. Lug on the inverter
  2. Lug on the Fuse
  3. The Fuse itself (class T 400A)
  4. The other lug on the fuse
  5. The lug on the battery disconnect switch
  6. The switch itself
  7. The other lug on the battery disconnect switch
  8. The lug on the bus bar (to be installed)
  9. The other lug on the bus bar
  10. The lug on the battery itself

So just on the positive cable, there will be 10 lugs (connections) total. I suspect that each connection, even if perfect, adds resistance. On top of that, I would estimate the total length of 2/0 cable with 10 connections to be 10 feet, and that alone will add resistance.

But here’s the thing, the more I think about it, the reason the shunt has it’s temperature/voltage connector on the positive battery terminal is so that it bypasses the entire inverter wiring and gets the voltage straight from the battery, right?

Since the BMS and the battery terminals spec out exactly the same, why is there a voltage discrepancy at the shunt?

Think of the bottle I described a few posts ago: With this voltage profile, there can’t be any significant voltage difference between the cells. Only pay attention to the cell voltages when a cell is between 3.4V and 3.45V. That’s when the voltages start to diverge due to the different levels of charge. And the current mustn’t be too high either.

The BMS shows the voltage across the series connection of the cells. The shunt shows the voltage at the battery terminals. There is a MOS switch in the BMS that disconnects the cells if one cell has a voltage above 3.65V. The cell voltage then slowly drops. That’s how such a large voltage difference occurs. If there is a large voltage difference, you need to immediately check the current, cell voltages and state of charge. With such a large voltage difference, the system couldn’t possibly function properly. I planned an expansion for a friend. There’s now 17m of 2/0 cable and a 160A fuse installed in the circuit. At 70A, that gives a voltage drop of 0.5V

As a general rule, you don’t replace anything without measuring first. This is important in order to be able to demonstrate an improvement. If you cut an old cable and remove the insulation, you’ll sometimes find that the copper has changed colour. It may look dark, black or greenish-blue. The first happens if the copper got too hot or if water had got in. The second happens if battery acid had got in. The result is that the wires are coated with a poorly conducting layer. Then, after fitting a new cable lug, it can happen that not all the wires make contact. The cable may not be very thick, but the effective cross-section is too small!! The best thing is to sketch a wiring diagram that includes all the cable lengths and cross-sections. Then set measurement points and get as much current as possible flowing. At least 20A. You can then use a multimeter on the millivolt range to measure voltage drops. Then you need to calculate the voltage drop based on the cable length, cross-section and current, and compare it with the measured value. If there aren’t any major differences, take another measurement while moving the cables back and forth. This reveals loose connections.

That’s a lot of connections. My coach used 4/0 over 8 feet for 12V.
For reference, 2/0 cable has a resistance of 79 uOhms per foot (at room temperature). At 100amps, that’s ~8mv of drop for each foot of cable. (4/0 would be ~5mv per foot).

If you load up your inverter so your DC is a steady 50 or 100 Amps, and measure along the cable length from bolt to bolt, you might find it’s just one section or connection that’s bad. If you find one section that’s really high, go from the bolt to the lug, then lug to any exposed cable past the crimp. It will narrow down where the drop comes from. Check across any closed switches too. You might find they aren’t closed as tight as you want.

I have an old 7 digit voltmeter. You can even see the current gradient in the lugs by looking at voltage that way.

As always guys - many thanks for the great advice! I pay attention to ALL of it, anything I skip over I come back to later :grinning_face: - and implement!

Major milestone yesterday. I rewired a lot of the battery bay (cleanup and new cable lugs almost everywhere). I also installed two new battery disconnect switches, one to replace the melted OE Guest switch, and another for a solar cut-off. I then changed the wiring around a bit so it made more sense and is cleaner, bearing in mind storage when you tend to shut off the battery disconnects and how it should function in that situation.

Here’s a pic of the ‘new’ battery bay. It’s 99% done. Just some minor cleanup and change where the Cerbo gets power. Another bus bar was added so I only had one 2/0 cable going to the positive post on the battery (and for other reasons). The replacement disconnect and bus bar is on the left, and the solar one is mounted on the rear wall.

I was at it for a while yesterday and into the night. I also got a Mopeka hockey puck for the internal propane tank, calibrated it, and got it installed and accurate, and then put one on the diesel tank, and they seem quite good.

It occurred to me the night before I did the work that it was likely that fixing every connection may not even address the voltage and SOC discrepancy. I could not get that shunt to do its job with the accuracy I was after, no matter what.

SOC was close but voltage was always hit or miss and seemed to vary depending load and whether it was charging or discharging. And this was the thing, no consistency. I could never make sense of it.

The new LifeP04 battery BMS highlighted that, and it is accurate. I mean, really, really accurate.

To that end, late last night I took a really close look at dbus-serialbattery. I set up a configuration file, installed it, and voila - perfect connection over the battery’s BlueTooth and it passed everything over. I can’t believe how much of the BMS is exposed to Victron. Even my MPPT’s are all pre-configured by the BMS. I think the only two settings you can change on those now are absorption voltage and float. Everything else is pre-selected and it shows, ‘controlled by BMS’.

As to the original issue, battery voltage and SOC - they are now exact. My multimeter shows .01 variance between the what the Victron GUI is showing measured at the battery. This has had a massive effect on everything, I now seem to be able to use the entire battery, it’s back to being very hard and time consuming to kill :grinning_face:

I suspect the SOC was really far off with the shunt and that it was never getting down to the 20% cut-off because it seemed the battery was always charging. The config file for dbus-serialbattery allows you to control a great deal. The Cerbo hooked up to the BlueTooth on the BMS with no issue, and on re-boots it’s reconnected every time. Mind you, if you look at the pic the Cerbo is about 3 feet from the battery!

So I didn’t need to make a custom cable, either RS485 or Canbus, it turned out to be as simple as minor alterations to the config file and then loading the driver into the Cerbo and rebooting it. Everything exposed in the Cerbo interface and selectable.

This turned out to be a real game-changer, it didn’t just nail down the voltage and SOC issues, it brought a whole new level of configurability to the table. But I am certain of one thing, I was never getting to use the whole battery, it’s as if it’s been super-sized.

Now I can see the discrepancy between the Shunt, the Inverter and the battery;

I’m pretty stoked about this, it’s turned my already excellent battery into the equivalent of a very expensive unit with native Victron compatibility.

I am troubleshooting an issue with it only charging to 50% or so, and I’m not sure where that’s come from (yet) but I’m really impressed with what has been exposed from the BMS to the Victron ecosystem.

That driver works great. It takes a bit to get it tuned for your system to throttle current and switch to float. In the past the BT connection wasn’t so stable, maybe they got it fixed.

Wait until you discover virtual switches in Node RED.

Don’t get me started!! :face_with_spiral_eyes: I’m trying to wrap this up :woozy_face:

I’m pretty sure I saw some things in my travels indicating work was done on the BlueTooth side of the driver. It’s only been a day but it’s been solid surviving reboots and everything.

I think I found out why it stopped charging around 50% or so. I had a whole bunch of DVCC settings turned on. According to the docs, you should only have DVCC enabled and the battery set as the controlling BMS…like so;

My guess is that they were ‘fighting’ but I don’t know for sure. I also used my new disconnect switches to kill power to the inverter and the battery and then turned off the battery using it’s switch (who ever would have thought you’d have an on/off switch on a battery?).

It’s now charging up fully. A lot of these errors I make are because I don’t really understand what I’m working with or how it works, so a lot of trial and error, but I figure if I post this stuff up it will help others.

Hey Paul, are you using that serial driver yourself?

I’m having some issues so I reverted the Cerbo back to an earlier firmware that should be working fine with it but now it has the bluetooth issues you were mentioning.

Also, I cannot seem to ascertain that it works with the ignore ac virtual switch.

Mr. Manuel hasn’t found the cause of the problems. He’s given up. As a test, I connected my batteries (Jk-BMS) via Bluetooth to a Raspberry Pi running VenusOS and Dbus-Serialbattey. It’s unreliable. A friend wants to connect his new battery to it so that I can see the cell voltages, battery temperature and the temperature in the battery enclosure. However, this will be a separate installation that doesn’t control the MPPs. If the MPPs are controlled by it, they’ll shut down for safety reasons if the connection drops. In that case, you should definitely use the RS485 connection. It’s considerably more reliable.

I didn’t see any BlueTooth issues with 3.85 and the latest public driver. I only got them when I tried to troubleshoot an issue and reverted back to 3.75 (?) with the same driver.

Mr. Manuel got in touch with me last night and suggested trying the nightly build instead of the release version. So I upped the Cerbo back to 3.85, installed the nightly, and everything got fixed.

I’m now able to see the diagnostic screen and can even activate the battery switch through the GUI and even manually reset the SOC on the BMS to 100% - among a ton of other things. So it’s clear that he’s done a lot of work since the public release. There’s a lot more functionality and it’s really well done.

I’m back to seeing zero BT issues. What seemed to introduce the BT issues was reverting the Cerbo firmware.

So I’m very close to being done and having the perfect control I’m looking for. The LifePO4 battery install really threw a variable into the mix that I had to adjust for. I’m still adjusting for it. But having the BMS connected absolutely fixed all of my issues…but it added another variable and learning curve. And to be honest I’m still struggling with the basics of BMS control.

The issue I’m having, and it’s the BIG one, is that my Virtual Switch config for the multi, Ignore AC input, does not seem to be working at all and seems to screw it up. And this feature is essential. It allows me to very easily control the balance between using the grid and solar to absolutely maximize the solar side and minimize the grid.

It’s the last hurdle in this journey but I don’t really have a grasp (yet) on the basics of BMS management. This causes me to wonder if Ignore AC is actually supposed to, or should work with BMS management or if the two are mutually exclusive?

If I disable Ignore AC then functionality of the serial driver appears to be 100%

This is the functionality I’m looking for (which doesn’t seem to work with the serial driver) and I could really use some help with understanding why;

The nightly build had the same problems. I also formatted the SD card again and installed Venus 3.71 and Dbus-serialbattery. At first, it looked good. But last night it stopped working again, even though Connected=yes and Staus=running. Even the (incorrect) cell voltages were still there. But the Raspberry Pi had no problems. I’ll try the nightly build again.