System: 2x 5KVA MultiPlus II in parallel, BYD LVS 24kWh batteries, Cerbo, SmartSolar MPPTs.
I want to switch on the hot water cylinder circuit dependent on battery state of charge, e.g. HWC on at 95%, HWC off at 90%. I also want the circuit to be switchable through VRM relay switches.
Two questions:
Can I use the K1 relay on the master inverter to drive a 12VDC contactor, which in turn drives a 230Vac contactor to turn the cylinder on and off?
Can I run the 12VDC + from the K1 through the Cerbo NC relay and then to the 12VDC on the contactor so the circuit is switchable remotely?
If there is a better way to do it, please let me know!
Using AC Out 2 and switching it using an Relay Assistant using SoC running the inverters is another alternative. You can get clever and hook an Aux input on the inverter to Relay 2 on the Cerbo, and then use Node-RED to control it.
But as @BjoernK suggested, doing the control logic somewhere else (Shelly + Node-RED on the Cerbo) can be easier.
Also, I believe the Shelly switching is soon to become much easier if you don’t want to play with Node-RED.
I prefer using Shelly‘s for non-critical control and high frequent switching, as it is easier to replace if the relais is damaged.
For critical, rare switching e.g. emergency disconnect I go for MP2 or Cerbo internal relais.
For those uses cases I do not want to rely on network working properly.