I am designing an off-grid system for Mallorca using:
- 4 × SmartSolar MPPT RS 450/200
- 28 × Pylontech US5000 (CAN-BMS, DVCC enabled)
- AIKO Neostar 3P+ A480 modules
- Module Voc = 40.9 V, Voc temperature coefficient = -0.22 %/°C
- 10 modules in series per string
The minimum ambient temperature at the installation site is about +2 °C. A temperature below 0 °C would be extremely unusual.
Therefore:
- String Voc at 25 °C = 409 V
- String Voc at +2 °C ≈ 430 V
- This is below the absolute 450 V limit.
However, the RS450/200 manual states:
“The maximum open circuit voltage of the PV array must be less than 8 times the minimum battery voltage when at float.”
With the Victron/Pylontech recommended float voltage of about 51 V, this would limit the array to approximately 408 V, which would rule out many otherwise valid 48 V system designs.
My questions are:
- Is the 8× float voltage requirement a hard operating limit or a conservative design recommendation?
- Does it also apply when the battery is managed by the Pylontech CAN-BMS with DVCC?
- Would this 10-module string (≈430 V Voc at +2 °C) be considered a supported configuration, or should I reduce the string to 9 modules?
Can the MPPT RS actually trigger Error 29 solely because the PV Voc exceeds 8 × float voltage, even though the PV voltage remains below the absolute 450 V limit?