I have a three-phase system consisting of six Quattro 15000s, with two in parallel on each phase.
I’m interested in updating the inverters using Remote VE.Bus firmware update.
I’ve shown one phase’s AC–out in the attachment.
The update instructions say there’s an intermediate stage where the inverters start up with the default settings before the configuration is loaded.
This raises the question: is it safe for the two inverters on the same phase to have their outputs connected while the system configuration has not yet loaded?
I’m confused by the wording of the instructions: first, the configuration is uploaded to the GX, then the firmware is updated, and finally the inverters are switched on in their default mode: “The settings will have been reset to their defaults”.
I assume the configuration is then loaded. But the system’s behaviour during this brief period isn’t entirely clear, especially since the AC-OUTs of each phase are connected together.
Download the remote config before you begin the process.
I am going to add here though, given it is not a simple system, just be prepared to have to plug on your MK3. Things can go wrong, it’s not often but they do.
So don’t go in without a backup plan. And knowing what settings you need to make for reprogramming.
There are no issues with the MK3; I disconnect the phases from one another until I configure the system.
I’m specifically interested in the procedure using Remote VE.Bus firmware updates. It says this is used for large systems, but the same manual also states that there is an intermediate stage when the system is switched on but not yet configured. This apparent contradiction is not explained at all, and it doesn’t say whether the outputs of parallel inverters need to be disconnected.
As I already wrote, the parallel and 3 phase configuration remains but the settings of each device will be reset to default.
You don’t have to do anything with the wiring but I would recommend to turn off the AC IN and AC OUT breaker during the update and reconfiguration process.
There is an manual with a video available for the update:
There must have been an error during the update. I’ve done updates several times on a system like the one the OP has, with six devices configured as a 3-phase system, two per phase.
There’s no difference compared with a 3-phase system.
If the devices are connected via VE.Bus, they won’t switch on until they’ve been configured as a system.
If you switch them on without VE.Bus, of course, each one will try to start up on its own, and you’ll get some unpleasant noises.
That’s why you switch AC IN and OUT on last; then, basically, not much can happen.
The noise isn’t pleasant, but they’ll shut down due to overload, or you’ll be standing right there to switch them off again straight away.
If one cable happened to be faulty among six devices, nothing would happen at first.
You’d need to have several faulty cables, and then they would also have to be connected in such a way that two parallel Multis each had no working communication connection to another one.
(If they’re the last ones in the chain, there would have to be two faulty cables.)
You first switch all the devices on in quick succession, and each one takes 1–2 seconds to start up.
As soon as two or more devices find each other via a working VE.Bus connection, they won’t switch on and will only show an error saying that they haven’t been configured for a system.
VE.Bus Error 3 – the Inverter and Absorption LEDs flash alternately.
The devices only switch on once the VE.Bus system configuration is complete.
But you should know all this if you’ve ever installed/configured a 3-phase system.
By the way, if you connect two Multis at AC OUT and switch on only one at a time, that won’t work either.
You’re worrying far too much again about something that would require several errors to occur at once for any damage to happen.
If you update a single Multi with VE.flash (or VictronConnect), the configuration of the system is deleted too, so you’ll have to set it up again.
Well, wire everything up… switch on the batteries first, then configure, and then switch everything on. I hadn’t really given much thought to what exactly happens if you do it in the wrong order.
What I didn’t know was that multiple Multis on the VE Bus won’t switch on if the system configuration hasn’t been defined.
Thanks for the detailed answer; you’ve put my doubts to rest. I always consider the worst-case scenario. I now understand that even then, the overload protection will kick in. Or I manage to switch off the output