I have used a Multiplus II inverter without a country selected in the Grid settings, and worked fine. The inverter ran as UPS, basically it would take power from the grid and charge a 48V lifepo4 battery. When grid failed, it switched to the battery.
But recently I added a MPPT, and some solar panels and I want the inverter to take power only from the battery when possible, and only use the grid if battery is at < 10%. For this I understand that I need to enable ESS, which requires a country to be selected for some reason. So I selected the country in the grid settings, added the ESS assistant, uploaded the new config, but now every time I connect to the grid, the inverter stops with an alarm “VE.Bus Error 11: Relay test fault”.
Switching grid country back to “none” makes the fault go away.
Any idea on why would this happen? Selected country is Romania, and it’s a fairly remote location with a TNCS electrical system.
In the ESS settings I disabled the grid feed, I do not want to inject any power in the grid, so that should not be the reason.
When looking at the VE Bus error details I see “BF safety test in progress - Failing step 8”. I assume this is some kind of back-feed test, right?
And for that specific step, on that page it says “check that line and neutral have not been swapped. Unlike non-grid code installations; line and neutral need to be wired correctly.”.. And I am 100% positive they are not swapped, so that cannot be the issue.
Could the lack of (good) local grounding have something to do with it? My grounding comes from the grid, basically PEN conductor gets separated into PE and N (before the inverter). So my local grounding should not matter, since grid grounding should be pretty good. And how would the inverter even know the difference?
If there is a voltage between neutral and earth, the inverter will notice and not connect.
This whether it is on acnin or AC out sometimes. I had a faulty appliance in one house that caused the error. So the line neutral can also be swapped inside the house wiring (non compliant and dangerous)
This is why the troubleshooting steps require wires to be disconnected on either side to test.