In Australia and New Zealand, lithium installations must be compliant to AS/NZS3004.2, which requires the BMS to give an audible and visual alarm at the normal operating position before a disconnection event. I’m working out the cleanest way to do that with the REC, and I’d like to hear from anyone who has already done it and had the system accepted as compliant.
I’m fitting an REC 2Q BMS (Victron CAN firmware) to a 24 V LiFePO4 bank, 2P8S, on a boat with a Cerbo GX, MultiPlus 24/5000 and MPPTs, all running under DVCC.
Specific questions:
-
Does the REC’s Victron protocol set any warning flags (frame 0x35A) ahead of opening its contactor, or only alarm flags at the point of disconnection? If it does send warnings, are the thresholds configurable? The 2Q manual only describes an alarm message sent just before the contactor opens.
-
Will the GX alarm relay (relay 1) operate on a warning from a CAN-bus BMS, or only on an alarm? I’ve seen reports of warning-level notifications showing on the display without operating the relay.
-
Has anyone used the REC’s two programmable optocoupler outputs to drive a light and buzzer directly as the pre-alarm?
-
My current plan is Node-RED on the Cerbo reading minimum and maximum cell voltage from the REC and driving relay 1 at my own thresholds, with the REC optocouplers wired to the same sounder as a hardwired backup. Has anyone had that arrangement accepted as meeting the standard, or been told it doesn’t?
Any experience with REC + GX and this requirement would be appreciated, including what you set the pre-alarm thresholds to, relative to the BMS disconnect points.