# RCD tripping on my ATLAS COPCO P8000T on connect

**URL:** <https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848>\
**Category:** DIY\
**Tags:** rcd, quattro-ii, beginner, generator\
**Created:** [5 September 2025 08:23 UTC](https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848 "2025-09-05T08:23:53Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![zebban](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/zebban/32/27959_2.png) [@zebban](https://community.victronenergy.com/u/zebban)\
**Post date:** [5 September 2025 08:23 UTC](https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848/1 "2025-09-05T08:23:53Z")

</div>

Hi,

My P8000T has a 30mA RCD. It trips when the QUATTROS II relays click to connect it.  
I tried to Google this, and I think it has its own MEN.

I have a 3-phase system with Quattro II, and the generator is on AC 1. The grid is on AC 2.

Is there an alternative way to make it work without disabling the RCD in the P8000T?

Best,  
Andreas

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/a/c/ac65106503e0677711b107f6f35d154b5946f955.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/4/3/437710fb59ef32d7cc1a4672f3b9bb58b273498a.jpeg)

---

<div class="post-metadata">

**Author:** ![zebban](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/zebban/32/27959_2.png) [@zebban](https://community.victronenergy.com/u/zebban)\
**Post date:** [6 September 2025 06:21 UTC](https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848/2 "2025-09-06T06:21:50Z")

</div>

I guess there will be a bypass operation next week 😅

---

<div class="post-metadata">

**Author:** ![MikeD](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/miked/32/1522_2.png) [@MikeD](https://community.victronenergy.com/u/MikeD)\
**Post date:** [6 September 2025 19:55 UTC](https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848/3 "2025-09-06T19:55:37Z")

</div>

No there is no other way than bypassing this, Victron inverters seem to have a sequencing problem with GFCI’s on the input and the grounding (MEN) relay in the Multi’s and Quatro’s.

---

<div class="post-metadata">

**Author:** ![zebban](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/zebban/32/27959_2.png) [@zebban](https://community.victronenergy.com/u/zebban)\
**Post date:** [12 September 2025 20:37 UTC](https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848/4 "2025-09-12T20:37:16Z")

</div>

@MikeD I did that, and now it works in bypass mode, charging the batteries. But it is about 53Hz unloaded and around 52Hz at 50% load.  
So the inverter is never active.

Enabling UPS, strange things happen, like drawing 10A from L1 for a few seconds and then disconnecting (Limit is 6A) . Can it still be a MEN problem?

How can I get Power Assist to work if the inverter is not active? Now I only have bypass and charging. Works in an emergency, but not what I want…

Best,  
Andreas

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/4/b/4b6db20e3eedd6d34cb0eb556790c26a340df65e.jpeg)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/7/d/7d73d7de87efad3f626749836f1b6ab4f5a14630.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/d/3/d379b8a6505e3eebe506825c10c58369fc12fb02.png)

TAB: General  
System frequency 50Hz  
Shore current 6.0 A  
Overruled by remote checked  
Secondary input shore current 25.0 A  
Overruled by remote unchecked  
Dynamic current limiter checked  
State of charge when Bulk finished 95.0 %  
Battery capacity 200 Ah  
Charge efficiency 0.95  
TAB: Grid  
Country / grid code standard Europe: EN50549-1:2019  
AC input 1 Generator (Grid code “Other”, no LOM detection)  
AC input 2 Above selected gridcode plus LOM B (compliant)  
Accept wide input frequency range (45-65 Hz) checked  
AC low switch mains off 195 V  
AC low switch mains on 205 V  
AC high switch mains on 248 V  
AC high switch mains off 253 V  
UPS function unchecked  
TAB: European grid code settings  
Use AUX1 as disable FeedIn signal unchecked  
Maximum AC current for charge or feed in 100.0 %  
Maximum generated apparant power 100.0 %  
connect waiting time 60 s  
connect power ramp 0.0 seconds  
low frequency connect value 49.500 Hz  
high frequency connect value 50.600 Hz  
low voltage connect value 85.00 % Un  
high voltage connect value 110.00 % Un  
re-connect waiting time 60 s  
re-connect power ramp 600.0 seconds  
low frequency re-connect value 49.500 Hz  
high frequency re-connect value 50.600 Hz  
low voltage re-connect value 85.00 % Un  
high voltage re-connect value 110.00 % Un  
rise-in-voltage protection U\> 110.00 % Un  
under voltage stage 1 85.00 % Un  
under voltage stage 1 delay 0.20 s  
over voltage stage 1 110.00 % Un  
over voltage stage 1 delay 60.00 s  
under frequency stage 1 47.500 Hz  
under frequency stage 1 delay 0.50 s  
over frequency stage 1 51.500 Hz  
over frequency stage 1 delay 0.50 s  
under voltage stage 2 80.00 % Un  
under voltage stage 2 delay 0.20 s  
over voltage stage 2 115.00 % Un  
over voltage stage 2 delay 0.20 s  
under frequency stage 2 47.000 Hz  
under frequency stage 2 delay 0.20 s  
over frequency stage 2 53.000 Hz  
over frequency stage 2 delay 0.20 s  
P(f\>) start frequency 51.500 Hz  
P(f\>) stop frequency 50.200 Hz  
P(f\>) start delay 0.50 s  
P(f\>) stop delay 0.00 s  
P(f\>) droop 5.00 %  
P(f\<) start frequency 47.500 Hz  
P(f\<) stop frequency 49.800 Hz  
P(f\<) start delay 0.50 s  
P(f\<) stop delay 0.00 s  
P(f\<) droop 5.00 %  
P(U) response Not used  
Reactive power regulation Use a fixed Cos Phi  
Filter time for reactive power 3.3 s  
Cos phi 1.00  
Use lock-in/out unchecked  
TAB: Inverter  
PowerAssist checked  
Assist current boost factor 3.0  
Inverter output voltage 230 V  
Inverter DC shut-down voltage 44.00 V  
Inverter DC restart voltage 48.00 V  
Low DC alarm level 48.00 V  
Do not restart after short-circuit (VDE 2510-2 safety) unchecked  
enable AES unchecked  
TAB: Charger  
Enable charger checked  
Weak AC input checked  
Stop after excessive bulk unchecked  
Lithium batteries checked  
Disable VSense (for diagnostic purposes) unchecked  
Configured for VE.Bus BMS unchecked  
Charge curve Fixed  
Absorption voltage 52.40 V  
Float voltage 51.00 V  
Charge current 50 A  
Repeated absorption time 1.00 Hr  
Repeated absorption interval 7.00 Days  
Absorption time 1 Hr  
TAB: Virtual switch  
TAB: Usage  
Virtual switch usage Do not use VS  
TAB: Assistants  
TAB: Assistant Configuration  
programmable relay (size:176)  
\*) Use ACOut 2 relay.  
\*) Set relay off  
\*) when Auxiliary input 2 is open for 1 seconds.

programmable relay (1) (size:37)  
\*) Use ACOut 2 relay.  
\*) Set relay on  
\*) when Auxiliary input 2 is closed for 1 seconds.

ESS (Energy Storage System) (size:1052)  
\*) System uses LiFePo4 with other type BMS  
(This can be either a BMS connected via CAN bus (e.g. a Lynx Smart BMS) or a  
BMS system in which the batteries are protected from high/low cell voltages by  
external equipment.)  
\*) The battery capacity of the system is 200 Ah.  
\*) Sustain voltage 50.00 V.  
\*) Cut off voltage for a discharge current of:  
0.005 C= 44.60 V  
0.25 C= 44.40 V  
0.7 C= 44.30 V  
2 C= 44.20 V  
\*) Inverting is allowed again when voltage rises 1.20 V above cut-off(0).  
\*) Relevant VEConfigure settings:

- Battery capacity 200 Ah.
- PowerAssist checked
- Lithium batteries checked
- Dynamic current limiter checked
- Storage mode unchecked

Total size of all assistants including the required  
(hidden) system assistants is: 1339  
TAB: Advanced  
limit internal charger to prioritize other energy sources unchecked

---

<div class="post-metadata">

**Author:** ![MikeD](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/miked/32/1522_2.png) [@MikeD](https://community.victronenergy.com/u/MikeD)\
**Post date:** [13 September 2025 20:28 UTC](https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848/5 "2025-09-13T20:28:16Z")

</div>

> [@zebban](#):
>
> But it is about 53Hz unloaded and around 52Hz at 50% load.

So: Time to tweak the governor of the generator. Gen should run about 52Hz at no load, and 50.5 - 50.8 at 50% load. I’m not familiar with setting up as quatro - I normally work with the MP2’s completely off grid. However, given that the low frequency / high frequency disconnect/reconnect appear twice in you above settings list, makes me wonder if these can be set differently for the 2 AC inputs, as one would expect\*. Seems that despite the wide frequency range box being checked, the gen frequency range is too restricted.

- On a faked setup, whilst input A can be set to a generator grid code - as you have done, input B cannot. However, while the transfer switch will accept “wide frequency range” the inverter is still probably restricted by the narrower grid code - disabling the power boost function.

Seems the only option here to get the boost function working would be to reset the generator frequency. However, depending on the gen type, reducing the RPM to correct the frequency may also reduce the output voltage. If this is the case, and the gen is capacitor regulated, then this (voltage) can be increased by increasing the value of the gen capacitor slightly. This may take some trial and error to get the machine correctly set. This is easier with AVR regulated sets - the voltage is independent of the frequency.

---

<div class="post-metadata">

**Author:** ![zebban](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/zebban/32/27959_2.png) [@zebban](https://community.victronenergy.com/u/zebban)\
**Post date:** [15 September 2025 11:22 UTC](https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848/6 "2025-09-15T11:22:06Z")

</div>

I assume this happens after the generator is accepted, and it must also apply to the other settings. In my case, if the frequency isn’t between 49.5Hz and 51.5Hz, the inverter won’t operate. That means no UPS function and no power boost. I believe it should be adjustable somehow, but I’m not sure how. I’ve tried reaching out for support by email, but haven’t received any response yet. It is a AVR block in the schematic. But looks like it’s only controls the voltage.

---

<div class="post-metadata">

**Author:** ![MikeD](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/miked/32/1522_2.png) [@MikeD](https://community.victronenergy.com/u/MikeD)\
**Post date:** [15 September 2025 18:51 UTC](https://community.victronenergy.com/t/rcd-tripping-on-my-atlas-copco-p8000t-on-connect/44848/7 "2025-09-15T18:51:10Z")

</div>

The governor screw that adjusts the frequency will be located between the top of the recoil housing, and the top of the air filter / Carburetor.

It’s a small screw that is easily adjustable.