Maybe there are some differences in different version of firmware. Their newer stuff behaves like this?
I have a seen a couple that sit high for over 20 minutes sometimes until the whole pack voltage goes up but these are on bigger banks and also on the famous daisy chain ones, so from what i have see it is not as cut and dry as that. And the whole bank voltage needs to be much higher before anything starts to happen.
They have passive balancers that are balancing with about 70mA max. (50 ohm resistors).
So, in order to balance a cell that, for example, itās about 1A behind, it takes about 14 hours topsā¦
As for the balance parameters, older, newer, all the same.
Anyone can see them by connecting to the console port of the battery and using the config command.
Standard: 3.36V, 30mV.
Hereās also some quotes from their technical department, on a discussion about a heavily unbalanced battery:
When the voltage difference is between 100-200mV, it means the battery could be balanced.
The balancing is successful when the voltage difference is below 30mV. It may take 12h to balance the battery. If the cells voltage difference is over 200mV, most of batteries couldnāt be repairable. When the voltage difference is over 30mV and cell voltage is over 3.36V, it will start balancing automatically.
Take a look at this Pylontechā¦
The charging current was set low, at about 8A, because the low the current is, the better the battery will behave when it has problems and you try to solve them.
Look how strange the min and max voltages have behaved, when the limiting charging algorithm kicked in at 23:00 in order to keep the max cell voltage below 3.52V.
At that moment the min cell voltage dropped and stayed even below 3.36V for a long period of time, with a voltage delta of 190mV !!!
Look at the charging current, when voltage was limited. Is only 100mA, the balancing current and some for the BMS.
But slowly the low voltage cell recovered and ultimately balanced, after 5 hours !!
Ignore the spike at 23:20, as it was a test from my part to see how the low voltage cell will behave.
So patience is gold in this case⦠In the end, all good things come to those who waitā¦
Update on the issue. Looks like overload was caused by voltage stabilizer. Tested several stabilizers with different firmwares, some behave more adequate some less. In the end, removing the stabilizer completely solved the issue.
From the grid, the victron can control what to connect to and what to reject and how much to load it. The LOM detection and avrs donāt do well. But for your load side the voltage is important to keep stable use the avr