Hello,

I’ve just bought a new house. It has a three-phase supply, but a single-phase heat pump has been installed on one of the phases (installed by a professional… we can only admire their duty to advise, especially since the model they installed is also available in a three-phase version…)

My Victron installation will be three-phase; can I also add an inverter in parallel on the phase in question, but not on the other phases?

For example, assuming the heat pump is connected to phase 1, the setup would be:

L1: 2 x MP2 5 kVA (i.e. 2 MP2s in parallel)

L2: 1 x MP2 5 kVA

L3: 1 x MP2 5 kVA

Is this type of configuration possible, or do I necessarily need 2 MultiPluses connected in parallel on each phase (6 in total)?

Thanks for your replies!

Technically, as far as I am aware, an advanced config like this can be built, but it is asymmetrical and local regulations may not permit it.
I would encourage you to talk to an experienced local supplier for advice.

Must for 3 phase configuration all mp have the same power? Otherwise one mp could be 8 kva.

They must be the same for each phase, for parallel they also must meet the compatibility code requirements documented in the 3-phase and parallel guide.

Hello,

your home has a three-phase supply, with phases L1, L2 and L3. If you install a three-phase Victron system, for example with three MultiPlus units, each unit is assigned to one of these phases. All three units must be the same type, including having the same power rating, battery voltage and firmware version.

Regarding your specific proposal — two 5 kVA MultiPlus-II units in parallel on L1, one on L2 and one on L3 — this asymmetric configuration is not supported in a three-phase Victron system with a GX device and VRM. You need the same number of MultiPlus units on each phase: either one per phase or two per phase, which means six units in total.

The entire DC side must also be sized for the combined power that may be demanded: battery discharge capacity, BMS limits, cables, busbars, fuses and battery isolators. Adding inverters does not increase the power that the batteries and wiring can supply. This check is particularly important when the grid is unavailable and the batteries have to supply all the loads.

The important thing is to distribute the larger loads as evenly as possible across the three phases. You can analyse the actual load distribution using the power data recorded for each phase in the VRM portal.

If your heat pump is single-phase, it draws power from just one of these phases. That, in itself, is not a reason to change the installation. The main things to consider are its electrical power consumption, any starting current, and the other appliances connected to the same phase.

When the grid is present and accepted by the MultiPlus, it can pass the grid supply through to the loads connected to its AC output. If demand exceeds the current limit set for the AC input, PowerAssist can provide additional power from the battery or from PV energy available on the DC side, depending on the configuration, battery state and available inverter power. In off-grid operation, the available power remains limited to the output of the inverter system.

If you haven’t ordered your Victron system yet, I strongly recommend discussing it with a professional before you buy. This will help ensure that you choose the right equipment and have it configured to suit your actual needs.

To start, explain what you want to achieve: increase your self-consumption, have a backup power supply, keep certain appliances running during a power cut, or become more independent from the grid. Based on that, a professional can tell you what’s feasible in your situation, which solutions would work and what the budget would be.

Best wishes from the Var,
Philip

Hello,

Yes, in hindsight, the type of setup I was talking about would cause an imbalance on the shared neutral, which could trip the RCDs, possibly even the main RCD.

I’m going to install a three-phase EV charger, so I’ll need to draw on the available capacity across all phases (including the one that might be taken up by the heat pump). Based on the documents included with the sale agreement, I checked the heat pump’s technical specifications. It will probably need to be installed across two different phases (one phase for the outdoor unit and another for the indoor unit), because the combined load exceeds 32 A, which is more than the current 18 kVA supply (i.e. 6 kVA per phase). In short, even without installing photovoltaic panels straight away, power assist will be a great help in managing the load, especially if the heat pump is running while the EV is charging, without having to opt for an absurdly high contracted capacity—or perhaps even allowing me to reduce the current one.

I haven’t moved in yet, so I’ll see what makes sense once I have a better idea of what’s been installed on each phase.