Hi All,
Looking for assistance with a Quattro-II 48/5000/70-2x50 (Product ID 2651) that has stopped working following a firmware upgrade from v556 to v560 through VRM.
The unit was working normally before the upgrade but is now reporting Fault with no AC output.
System:
-
Fully off-grid, no AC input connected.
-
Cerbo GX, 4 × Pylontech US5000 batteries and Victron MPPTs.
-
Batteries and BMS operating normally, no alarms.
Firmware upgrade:
-
Upgraded from v556 to v560 through VRM.
-
Update reported Error 733 (vbdup exit code 129) and Error 1512 (Insufficient rights).
-
Quattro now reports firmware v560.
-
Original v556 configuration was converted and successfully uploaded as a v560 configuration through Remote VEConfigure.
-
Multiple reboots performed without improvement.
Current symptoms:
-
State: Fault, no AC output.
-
VE.Bus Error: 0 when connected.
-
VE.Bus connection repeatedly switches between Yes and No, possibly indicating the unit is restarting.
-
Bulk, Absorption and Float LEDs flash together approximately 10 times, pause for 5 seconds, then repeat. All other LEDs remain off.
Troubleshooting completed:
-
Battery voltage approximately 50V, SOC 60–70%, no BMS alarms.
-
Physical switch ON and remote on/off jumper installed.
-
Virtual Switch disabled, no Assistants configured.
-
Inverter, charger and other configuration settings checked.
-
Original configuration restored successfully, but fault remains.
Looking for advice on:
-
What does the repeating 10-flash LED pattern indicate?
-
Could the failed update have left the firmware in an incomplete or corrupted state?
-
Is there a way to recover or reinstall firmware remotely through VRM/Cerbo GX, or is an MK3-USB required and what are the steps for both methods please.
The system was working correctly on v556 and is now without AC power.
Any advice would be appreciated.
Thanks,
Steve