I have a 50amp 120Vac generator and 120Vac shore power and I want to install a Victron inverter/charger down stream of those two items. I can install a selector switch to choose between the two but will a Quattro automatically switch between the two power sources? Thanks

---

<div class="post-metadata">

**Author:** ![Justin](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/justin/32/24_2.png) [@Justin](https://community.victronenergy.com/u/Justin)\
**Post date:** [25 October 2024 23:53 UTC](https://community.victronenergy.com/t/quattro-functionality/9034/2 "2024-10-25T23:53:38Z")

</div>

Yes, the Quattro has 2 AC inputs, and will automatically switch between them with priority given to AC-In 1. In many cases the generator will be installed to AC-In 1 and shore to AC-In 2 so that when connected to shore but preparing to leave dock/pedestal you can start the generator, the Quattro will switch to that AC input, and you can then disconnect shore power without ever losing AC input.