PV / Modbus Diagnostics

Hey all,

So we’re trying to diagnose some issues with modbus communication between the GX and an Enphase gateway / microinverter array.

A few questions that have come up:

  1. Is it still not possible to delete redundant entries from the PV inverter list on the console? It seems that Enphase has changed how the device presents and now I have multiple entries - I just want to delete them all and start again? I’ve seen several topics on the issue, including one where it was said that the functionality would be added, but I guess that hasn’t happened to date?
  2. Is there any detailed error log that will show connection errors etc.? At the moment the device just disappears from the VRM dashboard, but I’d like to see what’s happening behind the scenes, i.e. that the GX is trying to connect and being refused?
  3. Is there a way to eliminate the dependence on this modbus communication - which seems unreliable on the Enphase side - and just configure a CT block or energy meter phase to measure the current coming from the PV system instead?

Suggestions on the back of a postcard please.

Thanks!

Simply feed the, or any PV inverter through a suitable energy meter, such as an ET112, assign its role as PV inverter and all will be well …

That or something shelly meters.