I have an omnik 5kW pv inverter limited at 3.6kw and a multiplus 4k5.
The omnik and the multiplus wil share the same cable to the main distribution.
I want to connect the omnik to the ac out 2 of the multiplus so the maximum current will not exceed the limit of 16A.
I can’t connect the Omnik 5k to the ac out 1 because of the 1.0 rule and because the omnik doesn’t support frequency shifting power regulation.
Is it allowed to connect a PV inverter to ac out 2?
According to gemini this is not allowed due to arching when the contacts of the relay in the multiplus open while the pv inverter is delivering power, but I doubt the pv inverter will deliver a voltage high enough to cause arching.
The first PV inverter I found from them meets VDE-AR-N 4105 and therefore supports frequency shifting.
Perhaps you could post the model here again.
Or just configure it in the MultiPlus and test it gradually with a few hefty fan heaters as a load. Keep a close eye on the remote console as it approaches 100% SOC, and be ready to act quickly if it doesn’t curtail after all.
Please describe your setup a bit.
Do you have an ESS, an off-grid system?
Frequency shifting only comes into play in island mode.
My Hoymiles microinverters don’t really regulate the power either; it’s more a case of switching on and off. You can adjust the switching frequencies with VE.Configure.
I know, but when the grid fails the multiplus will use frequency shifting for regulating the pv inverter power. VDE-4105 should support that so I’ll try that.
Why not just install it on AC in?
Pumping power through a smaller ac out 2 relay and then yanking that if the grid was lost seems like too much risk for little reward.
If I’m interpreting this correctly, Victron changed the 1:0 rule from the original kVA rated power to the active power at 25 degrees Celsius. For the 4.5k model, that would be a maximum of 4 kW or 4 kWp.
Presumably, this change was made for a reason. It narrows the “grey area”.
The desire to charge the battery via the PV inverter if the ESS system fails is understandable. However, you have to consider whether the effort, costs and benefits are in reasonable proportion.
With a MultiPlus on what is presumably a three-phase grid, you won’t get very far anyway.
I would say that in Central Europe the grid is very reliable and stable, and extended off-grid operation is very unlikely.
In @JeroenSt’s case, it may be worth considering fitting the PV inverter with a blue 32 A plug and connecting it alternately to the MultiPlus input (as suggested by @nickdb) and, during off-grid operation, to the MultiPlus output (assuming frequency shifting works).
For this situation, I’ve drawn up an emergency procedure that also includes manual rewiring, and tested it.
A changeover switch could also be used instead of the plug. But you shouldn’t forget where the switch is. The problem I always see is: what can I take responsibility for when advising a layperson, and what would I do myself with my own system?
The fact that this 1:0 rule has been revised downwards gives me pause for thought. I think the likelihood of a power cut during periods of full sunshine is relatively high, since the grid may be shut down under these conditions due to overloading or overvoltage.
The only reason for this situation is that I have one cable with a maximum of 16A which the pv inverter of 5kW (limited to 3,6kW) and the multiplus 4k5 have to share.
Grid loss will not occur very often.
Because of this the victron has to monitor the current trough the cable to prevent overcurrent.
Putting the pv inverter on ac out 2 would disconnect the pv inverter on grid failure and prevents violating the 1.0 rule.
To connect the pv inverter to ac in, I would have to add an external current sensor to monitor the cable. That is an option, but it won’t be necessary if I can connect the pv inverter on ac out 2.