PV inverter on AC out 2

I have an omnik 5kW pv inverter limited at 3.6kw and a multiplus 4k5.

The omnik and the multiplus wil share the same cable to the main distribution.

I want to connect the omnik to the ac out 2 of the multiplus so the maximum current will not exceed the limit of 16A.

I can’t connect the Omnik 5k to the ac out 1 because of the 1.0 rule and because the omnik doesn’t support frequency shifting power regulation.

Is it allowed to connect a PV inverter to ac out 2?

According to gemini this is not allowed due to arching when the contacts of the relay in the multiplus open while the pv inverter is delivering power, but I doubt the pv inverter will deliver a voltage high enough to cause arching.

Hi,

An arc can occur, as it won’t necessarily be disconnected at the “zero crossing” in an emergency.

You could set up the MultiPlus as a microgrid for the Omnik to synchronise with.

If the Omnik is capable of black-starting, the Mutliplus will synchronise with it too.

Then you can use both, and the MultiPlus can charge your battery as well.

Just an idea.

Correct when ac2 out opens and closes.

No. That one is switched now. 32A is close the the 5kW so switched under load may be an issue.

5k is close enough to the 4k5 where the 1:1 is in a grey area so to speak in sizing.. The bigger problem is the lack of frequency shifting.

Is there no remote or other way to power limit the PV inverter?

Fortunately the Omnik is limited at 3.6kW so the current will be 16A maximum.

It doesn’t have a remote shutdown facility unfortunately.

I just quickly googled the manufacturer.

The first PV inverter I found from them meets VDE-AR-N 4105 and therefore supports frequency shifting.

Perhaps you could post the model here again.

Or just configure it in the MultiPlus and test it gradually with a few hefty fan heaters as a load. Keep a close eye on the remote console as it approaches 100% SOC, and be ready to act quickly if it doesn’t curtail after all.

It supports frequency shifting but afaik only on and off, no regulating between 0 and 100%

It is set to VDE-0126 but I can change that to VDE-4105 although that is not fully compliant with the Netherlands

Please describe your setup a bit.
Do you have an ESS, an off-grid system?

Frequency shifting only comes into play in island mode.

My Hoymiles microinverters don’t really regulate the power either; it’s more a case of switching on and off. You can adjust the switching frequencies with VE.Configure.

It’s an grid tied ess system behind a b16 breaker to the main fuse box.

Hi @JeroenSt

then the grid sets the frequency, not the Multiplus

Frequency shifting only comes into play during a grid failure in island mode

I know, but when the grid fails the multiplus will use frequency shifting for regulating the pv inverter power. VDE-4105 should support that so I’ll try that.

don´t forget to activate the pv inverter support at the ESS assistant before with ve.configure

Why not just install it on AC in?
Pumping power through a smaller ac out 2 relay and then yanking that if the grid was lost seems like too much risk for little reward.

If I’m interpreting this correctly, Victron changed the 1:0 rule from the original kVA rated power to the active power at 25 degrees Celsius. For the 4.5k model, that would be a maximum of 4 kW or 4 kWp.

Presumably, this change was made for a reason. It narrows the “grey area”.

The desire to charge the battery via the PV inverter if the ESS system fails is understandable. However, you have to consider whether the effort, costs and benefits are in reasonable proportion.

With a MultiPlus on what is presumably a three-phase grid, you won’t get very far anyway.

I would say that in Central Europe the grid is very reliable and stable, and extended off-grid operation is very unlikely.

In @JeroenSt’s case, it may be worth considering fitting the PV inverter with a blue 32 A plug and connecting it alternately to the MultiPlus input (as suggested by @nickdb) and, during off-grid operation, to the MultiPlus output (assuming frequency shifting works).

For this situation, I’ve drawn up an emergency procedure that also includes manual rewiring, and tested it.

A changeover switch could also be used instead of the plug. But you shouldn’t forget where the switch is. The problem I always see is: what can I take responsibility for when advising a layperson, and what would I do myself with my own system?

The fact that this 1:0 rule has been revised downwards gives me pause for thought. I think the likelihood of a power cut during periods of full sunshine is relatively high, since the grid may be shut down under these conditions due to overloading or overvoltage.

The only reason for this situation is that I have one cable with a maximum of 16A which the pv inverter of 5kW (limited to 3,6kW) and the multiplus 4k5 have to share.

Grid loss will not occur very often.

Because of this the victron has to monitor the current trough the cable to prevent overcurrent.

Putting the pv inverter on ac out 2 would disconnect the pv inverter on grid failure and prevents violating the 1.0 rule.

To connect the pv inverter to ac in, I would have to add an external current sensor to monitor the cable. That is an option, but it won’t be necessary if I can connect the pv inverter on ac out 2.

Have you considered using a Node Red relay and a digital input on the PV inverter to shut the inverter down when certain conditions arise.

Unfortunately this pv inverter doesn’t have that option.

Another option would be a contactor below the inverter that you control with a node red relay

Because the cable can handle only 16A and the multiplus together with the solar inverter can exceed this current and trip the breaker