Kia ora, I see what seems to be a contradiction between two sources of documentation of the PV Inverter Assistant.
- The PV Inverter Assistant itself has a setting “Restart PV Inverter when the (temperature compensated) battery voltage becomes lower than:”
- https://www.victronenergy.com/live/assistants:pv-inverter-support says “The frequency will reset itself automatically, in case one of the following conditions is met:
- the battery voltage drops below the re-bulk voltage threshold: the voltage that makes the system restart the charge cycle. For lithium batteries this threshold is defined as the float voltage minus 0.8V. Note that when float is configured to 54.8 volts or higher, then the battery voltage needs to drop below 54V. For lead batteries, the re-bulk voltage is defined as 5.2V below the configured float voltage. Unless that is configured to 56.8V or higher: then the battery voltage needs to drop below 51.6V.”
I don’t see how both can correctly represent the situation, and it would greatly help me to have clarity on this. Who can tell me how it actually works please (latest versions of VEConfigure3 90.04.251 and Multiplus firmware 2623558).
Thanks!