Pulse start/ stop onan marine genset

Trying to program 24v Quattro 2 5000 for gen pulse start and stop. Under assistant config. There was from memory a pulse setting. Sure I’ve done it before in victron configure.

[moderated. AI content removed as per our guidelines]

Hello,

Could you write a few lines about your system and your generator?

AI solutions often aren’t worth the time it takes to read them.

Quattro III 24v 5000 . Agm battery’s duel DCDC charges 17A. Mppt 30. All victron. Online vrm Cerbo. Onan 13.5kva back up gen. Duel diesel main engines. Not my installation.

Should the generator be started with the Quattro or the Cerbo?

What signals does the generator need?

Quattro as thats where assistance are.

The GX only has basic relay functions unless something has charged!

Normally you need a couple of time delay relays to generate the start/stop pulses, like these.

You have more options with the GX device.

There’s a whole chapter about it in the manual.

Even with a GX device (which I have) you need time delay relays if the genset requires pulsed start/stop signals (like my Kohler does).

Hi Ian

Thanks for your feedback. That exact part is described at the link in the GX manual.

Since @Smoothy hasn’t yet explained exactly how the generator’s remote start works, everything else is pure speculation. But we’ll figure it out yet :wink:

With Pramac, you also need both time relays..

Hi all, looks like pulse relay solutions is the best way. Thanks everyone for your input, suggestions and links. Much appreciated.