hello,
I have a connection problem with my MultiPlus-II GX.
As we live in a four-flat building, I only have the consumer unit
with RCDs, etc. in the utility room. Due to a lack of space, the
system is installed in the garage. The three-core cable from the Multi to the consumer unit
was installed and connected by the electrician.
The system consists of: 12 × 480 W PV panels on various roofs, Cerbo GX, MultiPlus-II GX, 2× MPPT 150/70, 1× MPPT 250/100, SmartShunt, and a VM-3P75CT energy meter. The system is configured as ESS.
I connected the VM-3P75CT current transformers under the main RCD to L1, L2 and L3, in the correct orientation, and the others to the 16 A circuit breakers.
The electrician connected the Multi’s feed-in cable via a separate RCD to the L3 that feeds into the main RCD.
Now I have the following problem!!
When I switch the system on, a cascading effect seems to build up.
The Multi keeps feeding in more and more current, even though the VM shows much lower consumption.
It ramps up to full power and feeds everything into the grid until the battery is empty.
If I remove a current transformer from L1, L2 or L3 and clamp it around the Multi’s incoming cable, everything works as intended on two phases, but the corresponding phase is then not included in the measurement.
Where is the fault??