Problem with Compact MultiPlus + MK3 USB not connecting to VE.Configure 3

Good morning, I’m having trouble connecting to my Compact Multiplus 12/800/35 (I’ve never connected to it before).
VE.Configure3 version 90.04.248 detects the MK3 USB but returns the following error:

  • MK3 detected (VE.Bus devices only)

The stickers on the unit show me these details *CMU 012801000* / *06430100061*
And on the chip I have this number, which must be the firmware: 1803133.VFF
It must be about 20 years old, but it’s in good condition and I intend to change the configuration for use with LiFePO4 batteries.
Could it be that the unit doesn’t support the MK3, even though the documentation says it does?
I have the MK3, and it works because I’ve programmed other units with it.

According to the manual, in section 5.3 Computer configuration, it says this:

5.3 Computer configuration
All values can be changed with a computer or a VE.Net panel (except for the multi-
functional relay and the VirtualSwitch when using VE.Net).
Some settings can be changed using DIP switches (see section 5.2).
To change the values with the computer, the following are required:

  • VEConfigure3 software: can be downloaded free of charge from www.victronenergy.com.
  • An MK3-USB interface (VE.Bus to USB), and an RJ45 UTP cable.
    Alternatively, the MK2.2b interface (VE.Bus to RS232) and an RJ45 UTP cable can be used.
    5.3.1 VE.Bus Quick Configure
    VE.Bus Quick Configure Setup (quick VE.Bus configuration) is a program with which
    a Compact unit or a system with up to three Compact units (in parallel or three-phase) can be
    configured easily. VEConfigure3 is part of this
    program.
    The software can be downloaded free of charge from www.victronenergy.com.

I’ve read everything I’ve been able to find on the forum, I’ve already tried several UTP cables, all industrial-grade, and I can’t connect.
I’ve also checked the issue of trying with battery only, in charger mode, in inverter mode,…

What options do I have left, any ideas?

I program the Mp using a bench power supply, so you can test the configured undervoltage alarms and shutdowns at the same time.

The Mp won’t switch on?

I think that is too old, I don’t see any 18 XXX series firmware updates in Victron Professional, even the 19XXX.vff had a small microprocessor and couldn’t do as much as later versions.

Sign up to victron professional and look at the resources: 1. Firmware
2. VE.Bus (Multis, Inverters And Quattros)

I wonder if a Mk2 USB would work?

Great that it’s still working though!

That MultiPlus is too old, you can’t use a MK3 for that, a MK2 should work.

You are very lucky to have such a old but gold device! good user :slight_smile:

Unfortunately, your device is not compatible with the MK3 interface. You need to use an MK2 interface instead. You can change the settings through VEConfigure.

Thanks for your contribution. I can already imagine it’s going to be difficult, but since the manual mentions using the MK3, I was hoping I’d be able to connect.
I’m not going to invest in an MK2. I’ve just found this on Victron Professional, which I think gives me an opportunity (the model I have is highlighted in yellow:

But having looked at the document, from what I can see, I won’t be able to do anything:

It’s a bit confusing, since it says my model is a 19XX, but according to the label on my firmware, which says 18xxx, it doesn’t seem to have VE.Bus. I’ll raise a query.

Another option is to see whether I can charge the new battery using the DIP switch configuration.
Based on the specifications of the battery I’m going to use, this configuration might work for me:

And these are the specifications provided by the manufacturer:

I’d like to know what you think of my idea. The BMS is Smart with BT, and I think I’ll be able to connect it to Home Assistant; if not, I imagine I’ll be able to adjust some settings in the app.

Thanks in advance.

Thanks, I’ll ask on Victron Professional, though I don’t hold out much hope.

If your label on the unit says 18XXX then it has an 18 series processor, not the 19XXX series processor, and also looks like you answered yourself, but there’s no Ve.Bus on the 18 according to the Victron doc.

It should work using dip switches, I have an old Skylla that set to just under my CVL using a multimeter to test it. For LFP you ideally want 3.45V per cell CVL (13.8V) maybe 3.5V (14V) is necessary if the BMS doesn’t start balancing until higher voltage, but to avoid over voltage protection of the BMS I wouldn’t go higher than their recommended 3.55V (14.2V). It does depend if you can adjust the BMS settings. Also if the dip switches allow much control - test with a multimeter though, it’s so old it may not be calibrated very well.

14.6V is unnecessarily high for daily cycling of LFP but lots of legacy auto stuff comes pre set at that.

Given what you say about the maximum charging voltage of 14.2 V, the DIP configuration wouldn’t work for me, as it gives 14.4 V. The manufacturer gives me values from 14.2 to 14.6 V, so the 14.4 V from the DIP configuration works for me, but not for your recommendation.

All I can do now is wait until I have the battery, then check the actual voltage during charging and the BMS configuration options.

Thanks for your input. I’ll bear it in mind and keep an eye out for the real-world tests.

There’s another drawback, which I don’t think is important. The MP gives me a fixed charging coefficient of C 0.26

14.4V isn’t a dealbreaker, but you can get 14.1V with the dip switches, you can also limit input current to 4A with dip. But I’d just look on ebay for an old Mk2-USB to programme it better for LFP. As 8 hour absorption is quite long and 13.8V float is also higher than an ideal float/maintenance voltage, but it will work.

The MK2 USB units I’ve found on eBay are quite pricey, almost the same price as in shops.
The documentation says it has to be the MK2.2b, but from what I can see it has an RS232 port, and I no longer have any equipment with a serial port. Would the MK2 USB work?
Regarding the 14.1 V, that’s true, it can be configured using the DIP switches.
I’m not too worried about the float voltage, as it’s going to be discharged and charged every day, since the idea is to make use of the battery charge.

So for now, I’ll try using the DIP switches while I look for an affordable MK2 to test.
I’d like to give the Compact Multiplus a second life.

The 4A / 12A issue refers to the AC amperage, right? So I’m not sure whether it affects the DC charging voltage.

Thanks for your input. With the help I’m getting, I’m getting a clearer idea of things.