Used power assist in mobile applications and that is configured in VE.Config. But, when in ESS mode its controlled with the following (as I understand it):

Limit Inverter Power in ESS menu

Limit system AC import current in peak shaving / Grid current limit

However some of these settings can be set in a few places, which one takes priority?

I am trying to limit the total power available to the house fuse box to 100A, example 60A from grid and the 40A from Multiplus (I already have 100A fuse on the consumer unit to protect it, but would also like to limit in the Multiplus.

Thanks,

Simon…

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [21 October 2026 12:11 UTC](https://community.victronenergy.com/t/power-assist-ess/64197/2 "2026-10-21T12:11:38Z")

</div>

T he grid limit wins, and the inverter limit is a separate cap on what the Multiplus itself can add.

Grid current limit (peak shaving / AC import limit): The system tries to keep grid draw under this number by topping up from the battery. This is the one that actually protects your fuse.

Limit inverter power: This caps how much the Multiplus can output. It doesn’t reduce grid draw. It just limits how much help the battery/inverter can give.

Possible problem could be: … If your house load is higher than (grid limit + inverter limit), the extra still comes from the grid. Nothing can stop that, because the power has to come from somewhere. Same if the battery hits low SoC: it stops assisting and the grid takes the full load.

So for your 60A grid + 40A Multiplus goal, setting both limits only works while the load stays under 100A and the battery has charge.

If you need a true ceiling, the Multiplus can’t enforce it alone. You’d use load shedding (AC-out 2 switching, or smart switches that drop big loads like the oven or EV charger when the total gets high). Or get a more capable system

The ess manual explains more about [peak shaving](https://www.victronenergy.com/media/pg/Energy_Storage_System/en/configuration.html#UUID-60cd4100-1eaa-ba1a-951a-cf0e5570d44f).

---

<div class="post-metadata">

**Author:** ![DJ-Dulux](https://avatars.discourse-cdn.com/v4/letter/d/3e96dc/32.png) [@DJ-Dulux](https://community.victronenergy.com/u/DJ-Dulux)\
**Post date:** [21 October 2026 18:21 UTC](https://community.victronenergy.com/t/power-assist-ess/64197/3 "2026-10-21T18:21:38Z")

</div>

@lxonline thanks for the great explanation, all makes sense now. The system has an upstream 60A DNO fuse, and a 100A to consumer unit in the property as thats all its rated at. We plan to do some shedding too…

Thanks…

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [21 October 2026 20:25 UTC](https://community.victronenergy.com/t/power-assist-ess/64197/4 "2026-10-21T20:25:51Z")

</div>

If the 60A is a hard limit, then still give it some head room.

For example when fuse sizing, it’s 1.25x  
In your case you are working backwards. You could probably pull 48 A continuously only. (48\*1.25 is 60A)

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [4 November 2026 20:26 UTC](https://community.victronenergy.com/t/power-assist-ess/64197/5 "2026-11-04T20:26:15Z")

</div>

Closed on 4 November 2026 20:26 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.