I believe there may be a firmware issue with the DC input low-shutdown and DC input low restart settings on systems with multiple inverter/chargers. I have tested this with several different Multiplus-II Systems but pretty sure it also applies to Quatro Inverter Systems and if needed I could test it.
The issue occurs when a system has 2 or 3 inverter/chargers, but only some of them are available to charge the battery.
For example, the settings shown in the screenshot are:
- DC input low-shutdown: 18.60 V
- DC input low restart: 21.80 V
If the battery voltage falls below the low-shutdown voltage, the inverter shuts down as expected. However, if only one of the inverter/chargers is subsequently connected to a charging source, the inverter will not restart and begin charging until the battery voltage has already reached the low restart voltage through some other charging source.
This creates a problem in several common configurations.
Example: 120/240 V Split-Phase System
We have two Multiplus-II inverter/chargers configured as a 120/240 V split-phase system, but we want to use a 120 V generator to charge the battery through only one of the inverter/chargers.
If the battery is charged before reaching the low-shutdown voltage, everything works normally.
However, if the battery reaches the DC input low-shutdown voltage, the inverter shuts down. Once that happens, connecting the 120 V generator to one inverter does not allow it to restart and charge the battery. The battery must first be brought back above the DC input low restart voltage by another charging source.
The same issue occurs with a 3-phase system if only one or two of the inverter/chargers are being used for charging. I have an existing customer with this issue on a 3 phase 120/208v system.
When all of the inverter/chargers are capable of charging, the system behaves as expected. It can even wake up and begin charging a lithium battery that has completely shut down due to low voltage. (I really like this feature!)
The problem occurs specifically when only a subset of the inverter/chargers is available for charging.
I have a system at our shop that I can use for testing purposes and can help with the testing if helpful. If Victron gets this fixed I believe it could be a great benefit.