We’ve started seeing a new error on our builds that we haven’t encountered before:
“Please set the VE.Can to a free number VE.Can interface - vecan0.”
Our current setup has a Wakespeed WS500 connected to VE.Can port 1, with a Victron terminator at the Cerbo GX and a Wakespeed terminator at the WS500.
When I check the VE.Can port 1 (VE.Can 0) settings, I see TX errors and error passive/bus warning errors. These error counts increase whenever I turn off the van’s ignition. The WS500 is ignition-controlled, so it appears the errors are related to the loss of communication when the WS500 powers down.
We recently updated the Cerbo GX firmware to version 3.85, but this issue appears on firmware versions 3.80 and newer.
I’ve tried changing the instance number, but the errors continue to be logged. I understand that the errors may be related to the loss of communication with the WS500, but this is the same configuration we’ve been using in our vans for almost two years without any issues.
A few questions:
-
Has the VE.Can network handling or error reporting become more sensitive in the newer firmware versions?
-
Is there a recommended way to configure the VE.Can interface to avoid these errors when the WS500 powers down with the ignition?
-
Is there a way to prevent the “Please set the VE.Can to a free number” message from appearing without changing our existing system configuration?
-
I also noticed a change in the device list. Previously, I only recall seeing one device, but now I see two: “Cerbo GX” and “WS500 Pro.” Is this expected behavior with the newer firmware, and could it be related to the errors?
Ideally, we’d like to resolve this without having to keep the WS500 powered on whenever the van’s ignition is off.
For reference, our system configuration is as follows:
-
Batteries: 2 × Epoch Elite 460 Ah (VE.Can port 2)
-
Inverter/charger: Victron MultiPlus-II 3000 VA (VE.Bus)
-
Alternator regulator: Wakespeed WS500 (VE.Can port 1)
-
Solar controller: Victron SmartSolar MPPT 100/20 with 200 W solar (VE.Direct)
-
Battery monitoring: 2 × Victron SmartShunt 500 A (VE.Direct)
Any guidance on the cause of these errors and the recommended configuration would be greatly appreciated, particularly if there’s a way to maintain our existing ignition-controlled WS500 setup.