I’ve had a MultiPlus-II 48 5000 GX on one phase for several years, charging Pylontech batteries using solar power. I’ve added Zendure SolarFlows on the other two phases to make the most of a new three-rate tariff (peak, off-peak and almost-free green hours). The Zendure SolarFlows charge their batteries when the rate is low and discharge them when it’s high. However, I have a problem: the MultiPlus starts charging the Pylontech batteries when the SolarFlows discharge theirs. This cancels out the benefit of the Zendure equipment. I need to prevent it from charging from the grid’s AC supply during peak hours. How can I do this? I have a USB-MK3.
I’d like the MultiPlus to be able to charge from the grid only between midnight and 6 am, and between 2 pm and 4 pm. I’d also like it not to discharge the Pylontech batteries during those times, except for the backup circuit.
I have two ET340 meters (one for measuring power to the grid and one for the panels and APS microinverters) to control the Victron equipment (Multiplus II 48/5000/70-50 and SmartSolar MPPT RS 450/100), and a SmartMeter 3CT meter for the Zendure equipment.
I’m trying to find out how to configure the Multiplus to charge the batteries from the grid during off-peak hours, but not during peak hours.
I’m trying to connect using my smartphone, both to VRM and to VictronConnect, but I can only see the readings, not the console with the menu that lets me take control. There is an MK3-USB, though. I can no longer connect to Vénus.local (error message: site can’t be reached).
With a 3-phase meter and a single phase inverter it will be trying to do phase compensation, so set ESS to individual phase control and not the total (sum) of all phases.
Scheduled charging is probably a good place to start, that is on the remote console under ESS settings.
why did you add Zendur and not a battery to the MP2?
Wouldn’t that have been cheaper per kWh?
I paid just under €120/kWh for my batteries (not Pylontech).