# Phase adjustment between generator and Multiplus required?

**URL:** <https://community.victronenergy.com/t/phase-adjustment-between-generator-and-multiplus-required/8983>\
**Category:** DIY\
**Tags:** generator\
**Created:** [25 October 2024 14:10 UTC](https://community.victronenergy.com/t/phase-adjustment-between-generator-and-multiplus-required/8983 "2024-10-25T14:10:26Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![Floki](https://avatars.discourse-cdn.com/v4/letter/f/34f0e0/32.png) [@Floki](https://community.victronenergy.com/u/Floki)\
**Post date:** [25 October 2024 14:10 UTC](https://community.victronenergy.com/t/phase-adjustment-between-generator-and-multiplus-required/8983/1 "2024-10-25T14:10:26Z")

</div>

Hello experts,

I would like to use a second Multiplus to charge the batteries from a generator via AC In. I have a needed Multiplus. This is configured on phase 1. Grid code removed and no wizard installed.

Does the generator also have to “generate” electricity on phase 1 or does it not matter?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [25 October 2024 15:08 UTC](https://community.victronenergy.com/t/phase-adjustment-between-generator-and-multiplus-required/8983/2 "2024-10-25T15:08:33Z")

</div>

You can have it in charger only mode, nothing connected to the output