Passthru means theres Mains available and switched through to the load side as well as the battery is not being charged or discharged, so its likely fully charged. The Multiplus is a simple connection, from mains to load, the inverter portion is “off”/in standby
I expect it to be in float and in absorbtion for an hour once a week. It did that upto 24 of december actually . But not anymore since. (After beiing off grid (inverting) for a day and going thru a normal charge cycle (bulk, absorbtion, float)).
It does work in power assist now and then, but slowly let the SOC go down
Passthrough can also happen when bms comms are not within certain intervals and if the bms senda a do not charge or do not discharge signal.
If the bms is in control it can also be the reason why there is a slow decline in soc. Some are both current and voltage controlled and do not increase the CVL sent to the system
I don’t know what the min rate is from the victron side.
But 30 seconds is in my opinion too long for decent control and information.
The gx will wait just over 2 or 3 minutes before logging a bms lost error. (Usually the time it takes to reboot the older slower devices and allow for programming tasks.)