# Parallel Multiplus ii 48/5000 UK - Not providing full power

**URL:** <https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366>\
**Category:** DIY\
**Tags:** parallel, multiplus-ii, diy, ess\
**Created:** [27 September 2024 09:07 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366 "2024-09-27T09:07:01Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [27 September 2024 09:07 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/1 "2024-09-27T09:07:01Z")

</div>

Hello,  
I hope someone can help / point me into the correct direction.

This is a ESS system which is running in the UK.  
Grid code is set to G99  
ESS Assistant installed on both units

This morning I noticed that the multiplus’s were discharging at around 4400w, even though the load exceeded this and it was pulling a considerable amount from the grid on top, around 2000w.  
The two multipluses should be able to provide the power no problem and have till this point.  
I have tried restarting everything, however this didnt change anything.  
Multiplus’s are running version V552 - Master Unit HQ23156EGX3, Parallel Unit HQ2207HVRTM.

I have 2x Seplos mason batteries proving 28.8kW of storage.

I have provided a screenshot as an example.

 ![Screenshot 2024-09-27 at 09.54.33](https://europe1.discourse-cdn.com/victron/original/2X/4/4ec873ae61f4ae21c4e136d9532b508d6499f4ab.png)

---

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [27 September 2024 09:33 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/2 "2024-09-27T09:33:50Z")

</div>

![IMG_9554](https://europe1.discourse-cdn.com/victron/original/2X/f/fc530f8513111e4e28cd5deab111fed1b17673fe.png)  
Here is a better example. It always leaves a considerable amount being pulled from the grid.

---

<div class="post-metadata">

**Author:** ![Daza](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/daza/32/29371_2.png) [@Daza](https://community.victronenergy.com/u/Daza)\
**Post date:** [27 September 2024 09:34 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/3 "2024-09-27T09:34:42Z")

</div>

Long Shot have you got DESS enabbled?

---

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [27 September 2024 09:39 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/4 "2024-09-27T09:39:15Z")

</div>

No, I don’t. I have some node red running which makes sure I export at maximum. But that doesn’t kick in till the battery SOC is at 95%

---

<div class="post-metadata">

**Author:** ![Daza](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/daza/32/29371_2.png) [@Daza](https://community.victronenergy.com/u/Daza)\
**Post date:** [27 September 2024 10:00 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/5 "2024-09-27T10:00:23Z")

</div>

You gone through your Nodes? and have you got a switch on the node so that you can return the multiplus to normal and then disable them and go from there?

---

<div class="post-metadata">

**Author:** ![rodwave](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/rodwave/32/3814_2.png) [@rodwave](https://community.victronenergy.com/u/rodwave)\
**Post date:** [27 September 2024 10:14 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/6 "2024-09-27T10:14:36Z")

</div>

> [@youmustcomply](#):
>
> Hello,  
> I hope someone can help / point me into the correct direction.
> 
> This is a ESS system which is running in the UK.  
> Grid code is set to G99  
> ESS Assistant installed on both units
> 
> This morning I noticed that the multiplus’s were discharging at around 4400w, even though the load exceeded this and it was pulling a considerable amount from the grid on top, around 2000w.  
> The two multipluses should be able to provide the power no problem and have till this point.  
> I have tried restarting everything, however this didnt change anything.  
> Multiplus’s are running version V552 - Master Unit HQ23156EGX3, Parallel Unit HQ2207HVRTM.
> 
> I have 2x Seplos mason batteries proving 28.8kW of storage.
> 
> I have provided a screenshot as an example.

Hi! It sounds like there may be a configuration issue or a fault with the multiplus units. Check the settings for load sharing and ensure that both units are properly communicating; consider reaching out to the manufacturer for further diagnostics if the problem persists.

---

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [27 September 2024 10:54 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/7 "2024-09-27T10:54:10Z")

</div>

I’ve disabled the node red stuff at the moment just to remove that element from fault finding.

---

<div class="post-metadata">

**Author:** ![WhiteCitySolar](https://avatars.discourse-cdn.com/v4/letter/w/b9e5f3/32.png) [@WhiteCitySolar](https://community.victronenergy.com/u/WhiteCitySolar)\
**Post date:** [27 September 2024 10:59 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/8 "2024-09-27T10:59:40Z")

</div>

How are you metering the grid side and PV inverter?

---

<div class="post-metadata">

**Author:** ![Mysik](https://avatars.discourse-cdn.com/v4/letter/m/c77e96/32.png) [@Mysik](https://community.victronenergy.com/u/Mysik)\
**Post date:** [27 September 2024 11:06 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/9 "2024-09-27T11:06:31Z")

</div>

Are you using grid meter (ET112 or VM-3P75CT)? Or are you using CT clip to measure the grid?

---

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [27 September 2024 11:22 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/10 "2024-09-27T11:22:55Z")

</div>

So the grid is being monitored by a ET112 and the solar is being monitored by Modbus. The DC solar is just charge controllers directly connected with ve direct cables.

---

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [27 September 2024 11:24 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/11 "2024-09-27T11:24:17Z")

</div>

Where would I find load sharing settings?

---

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [28 September 2024 17:08 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/12 "2024-09-28T17:08:06Z")

</div>

Small update - I shortened the USB for the ET112 to 20cm just to make sure this wasn’t the issue. No difference.

I tried downgrading the code on the cerbo to v3.32

The other thing that I have noticed it seems to behave like this when exporting too. So when there is plenty of sun it’s charging the battery but also dumping about 10% to the grid.

 ![IMG_9588](https://europe1.discourse-cdn.com/victron/original/2X/a/a702c1992e1ab5a9ef98425fe671e5a2f6d5a519.png)

---

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [30 September 2024 08:47 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/13 "2024-09-30T08:47:34Z")

</div>

Morning,

I have narrowed the issue down. This excessive grid use is only apparent when I have ACOut1 connected. Removing this connection on both inverters sorts the issue out completely.  
Now I am stumped, any ideas?

 ![IMG_9624](https://europe1.discourse-cdn.com/victron/original/2X/a/a782590c7f97a4bbfffad8f9f16e8ec88080ec6c.png)

---

<div class="post-metadata">

**Author:** ![youmustcomply](https://avatars.discourse-cdn.com/v4/letter/y/5daacb/32.png) [@youmustcomply](https://community.victronenergy.com/u/youmustcomply)\
**Post date:** [2 October 2024 10:53 UTC](https://community.victronenergy.com/t/parallel-multiplus-ii-48-5000-uk-not-providing-full-power/5366/14 "2024-10-02T10:53:01Z")

</div>

Now I have narrowed the issue down, I will open a new thread.