# Our Multiplus inverter is overheating

**URL:** <https://community.victronenergy.com/t/our-multiplus-inverter-is-overheating/42985>\
**Category:** DIY\
**Tags:** beginner, not-listed\
**Created:** [12 August 2025 17:45 UTC](https://community.victronenergy.com/t/our-multiplus-inverter-is-overheating/42985 "2025-08-12T17:45:40Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![Mjfielding](https://avatars.discourse-cdn.com/v4/letter/m/5f9b8f/32.png) [@Mjfielding](https://community.victronenergy.com/u/Mjfielding)\
**Post date:** [12 August 2025 17:45 UTC](https://community.victronenergy.com/t/our-multiplus-inverter-is-overheating/42985/1 "2025-08-12T17:45:40Z")

</div>

When I am connected to shore power my two inverters are overheating, why?

---

<div class="post-metadata">

**Author:** ![1234enough](https://avatars.discourse-cdn.com/v4/letter/1/ea666f/32.png) [@1234enough](https://community.victronenergy.com/u/1234enough)\
**Post date:** [12 August 2025 19:01 UTC](https://community.victronenergy.com/t/our-multiplus-inverter-is-overheating/42985/2 "2025-08-12T19:01:36Z")

</div>

Little more detail would be good.

Ambient temp / how is the location of inverters ventilated / are inverter internal fans running or are they disabled with silent assistant ? / what charge or load are they doing.

How have you determined they are overheating? They should derate the hotter they get.

---

<div class="post-metadata">

**Author:** ![dognose](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dognose/32/968_2.png) [@dognose](https://community.victronenergy.com/u/dognose)\
**Post date:** [12 August 2025 19:03 UTC](https://community.victronenergy.com/t/our-multiplus-inverter-is-overheating/42985/3 "2025-08-12T19:03:56Z")

</div>

Also check, if the heat may originate from a bad contactor / connection point down the wiring. If there is a high resistance contact somewhere, that could produce a significant amount of heat and distribute back through copper wiring easily.

Especially if both inverters are overheating at the same time, this may be the case.