Online ups with Multiplus and Pylontech batteries?

One customer was complaining about an unstable grid, voltages fluctuating alot, and getting his electronic equipment damaged all the time. One solution is to connect the grid to an online ups, which would continuosly filter the grid, converting ac to dc, then back to ac .

However we would like to do it with Victron Energy products, as he would like to add solar, wind to the system.

Is this possible using LiFePO batteries such as Pylontech ?

I would design the system as follows :

1 multiplus II 48/5000 connected only to the grid and the batteries
1 multiplus II 48/5000 connected only to the same batteries and to the loads
2x Pylontech UF5000 batteries
1 gerbo gx

This way the multiplus which is connected to the loads only is not affected at all by the anomalies of the grid.

However the question is how do I make the two multiplus listen to pylontech with one gerbo ? Do I have to install two gerbo’s ? in this case, how do I make sure that one pylontech system gives info to two gerbos ? As it communicates over canbus , this should be possible ?

Best Regards

Bülent

This is completely unsupported, though some have done it.
The gx can only manage one multi as well.
Multis are not a ups. They have some properties of a ups, but they do not smooth power and the failover is not as good as an actual ups.
If the gear is sensitive rather add a dedicated, ups on ac out.

1 Like

We use Multiplus as UPS at a number of sites and they work fine as an inline UPS. Reaction times to grid issues are fast enough to maintain suitable power to sensitive equipment.

If you were worried about voltage spikes affecting equipment then even if you have some sort of UPS you would want to consider a surge protection device to protect it upstream.

It is possible to adjust the voltage range the Multiplus will accept or reject the grid. This could be used to make the device more or less sensitive to grid fluctuations.
image

As Nick says there is no way to have two Multiplus show on a single GX. You could however connect the second inverter to the DC bus via a Smart Shunt which would give you power consumption. Further care would be need to ensure the inverter shuts down on low SoC as it won’t be able to see and of the battery information from the Plyontech.

1 Like

The challenge with the multi being a grid attached ups, while it is good enough for domestic purposes, some gear is more sensitive than others, and attached to a bad quality grid, you can get power dips as the output tracks the input. Voltage limits don’t seem to help much with brownouts, so if it is critical gear then either run it permanently off an islanded inverter or consider a specialist ups between the loads and inverter.

If its basic gear and you don’t care about a quick restart then the multi is fine.

1 Like

I have a graveyard of UPSs here all from established brands. The build quality of them is all lower than that from any Victron device. We had an expensive online UPS flat out die on us a year ago taking everything connected to it offline and just outside it’s warranty period.

Electronic devices are typically powered via a switched mode power supply which gives them a large range of AC input voltage as they cater for various global standards. The Multi should disconnect the grid before it is out of range for the PSU.

1 Like

Well, in my experience that isn’t always the case; if it can cause something as arb as a modern TV or POE switch, all with switch mode supplies, to dip then it isn’t ideal. Can’t say I have had many issues with APC/schneider gear as a core ups, though they do cost a bit.
For the most part the conditions that have caused a power dip are rare across the broad number of outages.
It is for that reason I will never attach server gear to these, but for telco/pop purpose it is adequate, few will notice the restart if it occurs and it is unlikely anything hung off these systems has a 100% uptime sla anyway.

1 Like

@bulent.aydin

Although are around the same price, you can use a battery charger instead of the first MP2.
But an MP2 used in charger only mode is also OK.

Although I didn’t tried, I suppose that two Cerbos can be daisy chained on the BMS-CAN with a single Pylontech and I suppose they will work, because there is no direct CAN frame from Cerbos to the Pylons, just listen to the Pylons broadcasts and a Victron presence broadcast.

I would do the following chain of equipments:

  1. Grid
  2. Simple charger with some minimal monitoring (Skylla TG)
  3. Pylons
  4. MP2 (or simple Victron Inverter, LowFreq or HighFreq)
  5. Cerbo for monitor MP2 (or Inverter) and Pylons.
  6. Sensible equipment
1 Like

Multiplus II 48/5000 is about half the price of a Skylla TG 48/50 in the UK currently. Plus it supports DVCC and will give you some telemetry on the state of the grid.

1 Like

Hi Alex ,

I will go for this solution. If successfull , I will tell in this discussion. I think that’s a good solution compared to other inline ups. Advantages are : Possibility of adding solar, wind , additional power , additional batteries.

1 Like

You can have a second ve.bus system appear on the cerbo and vrm for data logging by using a mk3-usb to ve.bus adapter.

Screenshot 2024-09-23 160422

I have tried this option in my previous installations, however the response seems not quick enough to protect the devices from the over/under-voltage situations.

Hello @dansonamission would cerbo be able to control both multiplus for charge and discharge current limitations coming from pylontech ?

would cerbo be able to control both multiplus for charge and discharge current limitations coming from pylontech ?

No. This is only for monitoring. The first system will be managed by the BMS (via DVCC), the other not.

1 Like

in this case, this is not so appropriate for me , as the first system should also be able to listen to the batteries.

Which is why Victron doesn’t support independent systems sharing a battery/GX.

1 Like

Your load side MP wouldn’t do any charging. And if you are 2x US5000 then unless you have some odd combination of events you won’t exceed their DCL.

The second MP is just a DC load for which there are solutions to manage.

1 Like

I’m using grid voltage stabilizers for the problem you mentioned. It stabilize voltage in vide range from 180 to 280 volts and gives 220v on output.

1 Like

What type of stabilizer are they?
How quick did they react?
Thanks!

It’s 10ms reaction time, inside is toroidal transformer that regulates voltage.
One thing to remember - not all of them supports two ways transformation, so need to be careful with systems that exports to grid

The ones that I have. You can translate page in browser to read specification Нормализатор напряжения VN-844, 11кВт 50А "ПРЕМИУМ 64", 136-265В от производителя. Купить нормализатор напряжения vn-844, 11квт 50а "премиум 64", 136-265в по лучшей цене в Киеве, Одессе, Украине.

Works fine for 4 years, very standard equipment in Ukraine when you own private house. Popularity is not connected with war, more with a grid quality, especially during winter times.

1 Like