Hello everyone,
A conversation with my wife recently got me thinking.
Following the acts of sabotage against infrastructure here in the Rhenish lignite-mining region, she remarked how reassuring it was that, with our PV system and battery storage, we would actually be well prepared for a prolonged power cut.
I then had to explain to her that, although our system has almost 25 kWp of PV capacity and more than 22 kWh of battery storage in total, it would nevertheless largely fail in an emergency. All of the PV inverters are SMA units and are grid-following. If the public grid fails, the entire PV generation therefore also shuts down. Unfortunately, the same applies to the existing SMA storage solution.
I am aware of this drawback. A complete solution with a three-phase islanded grid and continued PV operation would be a much larger project. More on that later. For now, I am concerned with a much smaller and more pragmatic solution.
Objective
For the time being, I do not want to make the entire house emergency-power capable straight away. I would nevertheless like to explore that conceptually as well; see the follow-up posts.
For an initial stage, the following loads would be sufficient for me:
- air-to-water heat pump
- groundwater well for the drinking-water supply
- chest freezer
- some lighting
- router, mobile phones and similar small devices
Existing Victron equipment
In addition to my SMA system, I already operate:
- Victron MultiPlus-II 48/5000/70-50
- Cerbo GX
- 15 kWh Felicity battery storage system
The MultiPlus currently operates exclusively as an AC-coupled storage system. The AC-Out has not been used so far.
(Details of the SMA/Victron setup are in the first reply to this post for anyone interested…)
My idea
I would like to use the AC-Out as a separate emergency-power network.
The following would be connected to it:
- a CEE 32 A socket for the heat pump
- several Schuko sockets for the chest freezer, lighting, etc.
- the groundwater pump
- if required, a cable reel for other important loads in the house
Generator
I would like to install a changeover switch on the MultiPlus’s AC-In:
Grid ↔ Generator
At present, I am planning to use a Könner & Söhnen KS 5500iES ATSR with remote-start functionality as the generator.
The generator would not supply any loads directly, but would exclusively supply the MultiPlus.
This would mean that all loads would always see the supply generated by the Victron. Depending on the situation, the energy would then come from the battery, the generator or a combination of the two.
The generator should only start automatically if the battery level becomes too low or the required power exceeds the MultiPlus’s continuous output.
Heat pump
The installed unit is a Nibe F2125-12.
The heat pump can easily be operated on a single phase. The phase used for this is protected by a 25 A circuit breaker, while the heat pump requires a maximum of around 20 A. The electric auxiliary heater would of course not be supplied in emergency-power mode.
I would install a changeover switch at the heat pump:
Grid supply ↔ Emergency-power supply
In an emergency, the heat pump would then be supplied via a CEE connection from the MultiPlus’s AC-Out.
The plan is to use a CEE extension cable approximately 15 m long with a cross-sectional area of 4 mm². It would only be run from the basement window to the garage when needed and would not be installed permanently.
The actual question
Am I overlooking any fundamental flaw in this concept?
I am particularly interested in experience with:
- using a MultiPlus-II as an emergency-power supply for a heat pump
- generator operation via the AC-In
- automatic generator control
- possible pitfalls or protection concepts
- anything that would immediately stand out to an experienced Victron user with this setup
I am explicitly looking for a robust and as-simple-as-possible solution for a prolonged grid outage, not yet a complete off-grid system for the entire house. I will discuss those considerations in the next posts.