Presently I’m preparing a MultiPlus-II for a grid-backup application (single phase, 230 V), in combination with battery and solar PV. The MultiPlus-II is intended to never feed back to the grid. All solar production will be used locally (on the DC side or AC side downstream of the MultiPlus-II). I would be very thankful if anyone can answer the following questions regarding how to ensure Norwegian grid code compliance?

  1. Is there already an applicable “Country / grid code standard” for Norway (or for example a general European setting) to select during MultiPlus-II setup?
  2. Does the MultiPlus-II fulfill an applicable standard to prevent feeding back to the grid in case of a grid power outage (I need to specify this for the grid owner)?
  3. Is any external device (for example from Ziehl) needed?

If you’re not exporting electricity, the grid code doesn’t apply to you. And yes, there’s the European standard EN50549-1.

Yes, the LOM function is there.

No, in your case, it’s not needed.

Thank you Diessel for your reply!

Regarding the second point, I would probably need to specify if the LOM function fulfills a certain standard. Could that be EN 50549? I found “Certificate ESS EN 50549-1 MultiPlus-II (GX) 3k & 5k”, where it says “Automatic disconnection with single fault tolerance is provided” and that it has been tested according to EN 50549-10:2022.

Regarding the third point, it makes sense what you write, but Victron’s manual “MultiPlus-II External Transfer Switch application” (https://www.victronenergy.com/upload/documents/MultiPlus-II_External_Transfer_Switch_application/179843-MultiPlus-II_external_transfer_switch_application-pdf-en.pdf) states in the table in section 1.4 that for Europe EN50549-1:2019, Ziehl relay UFR1001E required. Could that be only for systems with multiple inverters (as shown in the illustrations there)?

External transfer switch required for parallel operation of models above 8kVA

Thank you again. In the meantime, I have also received a reply by e-mail from Victron. As I interpret it, the LOM function fulfills EN 50549-1:2019 and has been tested according to EN 50549-10:2022, as I wrote before.

All certificates of conformity to various standards for Victron products are publicly available.

Just read the product descriptions carefully.