# Noob with MP2GX that won't turn on the inverter

**URL:** <https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754>\
**Category:** DIY\
**Tags:** pv-inverter, multiplus\_2\_gx, vrm\
**Created:** [9 October 2026 17:28 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754 "2026-10-09T17:28:09Z")\
**Posts on this page:** 8\
**Page:** 2

<div class="post-metadata">

**Author:** ![Wiggo](https://avatars.discourse-cdn.com/v4/letter/w/f05b48/32.png) [@Wiggo](https://community.victronenergy.com/u/Wiggo)\
**Post date:** [10 October 2026 20:03 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754/21 "2026-10-10T20:03:44Z")

</div>

Lol. 1985, I wrote my own OS for an 8080 dev system I built so I could enter machine code from a terminal then run it. Way quicker than burning it to an EPROM, realising it didn’t work, then blu-tacking the EPROM to the window for a week to erase it

---

<div class="post-metadata">

**Author:** ![Ems-Sonne](https://avatars.discourse-cdn.com/v4/letter/e/b19c9b/32.png) [@Ems-Sonne](https://community.victronenergy.com/u/Ems-Sonne)\
**Post date:** [10 October 2026 20:42 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754/22 "2026-10-10T20:42:02Z")

</div>

Hi,

yes, the MP2 configuration in VEConfigure really is old-school. I felt like I was back in Win98 too, in terms of the program design… I use the Cerbo GX as the control unit (more connections, etc.; it’s proven its worth).

Best regards

---

<div class="post-metadata">

**Author:** ![Wiggo](https://avatars.discourse-cdn.com/v4/letter/w/f05b48/32.png) [@Wiggo](https://community.victronenergy.com/u/Wiggo)\
**Post date:** [11 October 2026 09:36 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754/23 "2026-10-11T09:36:19Z")

</div>

OK, so the problem is mostly solved. My pet sparkie had plugged a CANbus lead into a VEbus port. Swapped them around and hey presto! it nearly works.

Despite everything I tried, I can’t get the system to see the VM-3P75CT over CANbus. I connected via ethernet and VictronConnect now sees it as a local device, but it doesn’t show in VRM portal as part of my installation. If I tell the GX to use the external meter, it just goes to pass thru and says it can’t find one. Any ideas?

---

<div class="post-metadata">

**Author:** ![stadtrand](https://avatars.discourse-cdn.com/v4/letter/s/8edcca/32.png) [@stadtrand](https://community.victronenergy.com/u/stadtrand)\
**Post date:** [11 October 2026 10:22 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754/24 "2026-10-11T10:22:45Z")

</div>

If the meter is connected via Ethernet, Modbus scanning must be enabled in the GX.

SETTINGS-\>INTEGRATIONS-\>Modbus Devices-\>Automatic Scanning = True

---

<div class="post-metadata">

**Author:** ![Wiggo](https://avatars.discourse-cdn.com/v4/letter/w/f05b48/32.png) [@Wiggo](https://community.victronenergy.com/u/Wiggo)\
**Post date:** [11 October 2026 10:26 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754/25 "2026-10-11T10:26:17Z")

</div>

Perfect, thanks!

---

<div class="post-metadata">

**Author:** ![Ems-Sonne](https://avatars.discourse-cdn.com/v4/letter/e/b19c9b/32.png) [@Ems-Sonne](https://community.victronenergy.com/u/Ems-Sonne)\
**Post date:** [12 October 2026 04:56 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754/26 "2026-10-12T04:56:13Z")

</div>

As an additional option, you can also configure the system so that it doesn’t require an external meter. However, this setting only ensures that if you connect something to AC Out, at least that part is powered by the battery. Otherwise, as you’ve already described, the system switches to bypass mode in general.

System → ESS grid meter required.

As long as the meter is available, though, the system will use it and also cover loads on AC In.

---

<div class="post-metadata">

**Author:** ![pau1phi11ips](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pau1phi11ips/32/1110_2.png) [@pau1phi11ips](https://community.victronenergy.com/u/pau1phi11ips)\
**Post date:** [12 October 2026 06:40 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754/27 "2026-10-12T06:40:02Z")

</div>

Glad you got it sorted over LAN. If you’re using the Can connections, make sure you’re using the Terminators too.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [26 October 2026 06:40 UTC](https://community.victronenergy.com/t/noob-with-mp2gx-that-wont-turn-on-the-inverter/63754/28 "2026-10-26T06:40:31Z")

</div>

Closed on 26 October 2026 06:40 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.