Noob again, can't seem to find any clarification on some bits for an MP2GX

Another noob question, sorry. Just got everything installed: MP2GX, VM-3P75CT, Pytes V16 (16kWA 48V battery). For additional fun and games, we have an old Rent-a-Roof 3.6kWp solar setup, which we are not allowed to touch - they get the FIT, we get the juice. It is all connected up as shown below:

Now, we’ve just completed our first 24 hours, and it sort of works. After it went live yesterday morning, grid consumption fell to zero, give or take a few Watts, and it was supposed to charge for 6 hours from 23.30 on EDF’s EV tariff (2330-0600). At some point overnight, I did see it was charging, so all good. However, at 0620 this morning, we were still consuming just over 3kW from the grid.

On a couple of occasions yesterday, and again this morning, VRM showed the system in bulk charge mode, when the schedule only has a daily 2330-0530 window for charging. Switching to Inverter mode made no difference, it still showed as charging. I had to turn off, then on, inverter and then on a few times, and it eventually decided to play. Any ideas?

I have searched, and found a handful of comments about setting scheduled charge times, and that even though they are enabled per schedule, from the Console>Settings>System Setup>ESS menu they are still marked as inactive. Is this a feature?

Finally, I only have V Out 1 connected, so how is the VRM App deciding I have both AC Loads and Essential Loads?


And how has it worked out that I have consumed 14kWh, yet taken 18.7 from the grid? How am I meant to interpret this? The graph pretty clearly show what went in as charge overnight…

AC In and AC Out should not be connected together, your diagram show a connection between the two, through the 20A and 16A MCB.

No idea on your chosen topology but:

  • AC Out_1 should be for consumers
  • Single difference between AC Out_1 and Out_2 is that Out_2 will be disconnected in case of mains failure. Both are showing in essential loads due to a single measurement device on the output. If no interest in disconnecting some consumers while mains are down, keep all on AC Out_1.
  • AC In should be tied to mains through MCB, as well as your existing PV installation, which was mentioned as a no touch zone.
  • I see 3 power meters in your diagram, what is the role of the “Smart Meter” in the lower left corner ?

Right, so the easy part is the meters: The smart meter, bottom left is the DNO supplied main meter that they read remotely every 30 minutes. The generation meter in the loft measures the output of the PV inverter, has a modem and SIM card sends readings to the solar people so they can claim their FIT. The VM-3P tells the MP2GX whether we are consuming from or exporting to the grid.

The old PV inverter uses V In to synchronise with the grid, and automatically disconnect if the grid is off, so we are not feeding power into a circuit the DNO thinks is isolated. I initially assumed the MP2GX did the same.

V In to the MP2 is via the same 16A MCB as the PV inverter, so one breaker shuts down everything. As we have no interest in running as a UPS, I guess everything should come from V Out 2 so the inverter can’t try and feed back to the grid in the event of a failure. I did query why it wouldn’t treat its own output as V In, but the supplier assured me it didn’t. There is no way I can rewire the house to take the entire 100A feed to V In so it can pass it through, besides the obvious issue of connector sizing!

The output of the MP2 is fed back into the DB via a 20A MCB as that would correspond with approx 5kVA output..

But now it seems that I cannot wire this puppy up to drop if the grid goes down, meaning if the DNO isolates us for maintenance, they are getting a nasty surprise, right? How else would you approach this?

No. You configure a grid code, the inverter does LOM detection and disconnects when mains drops or exceeds thresholds.
I would suggest it is worth your while to go through the basic online video training at professional.victronenergy.com. It will fill in most of the fundamentals for you.

OK, just ran Remote VEConfig, it is currently set with G99/1 and LOM Type B. Still unsure how to separate V In from V out, though

For a proper answer please explain, in detail, your intention/system required purpose.

Up to now it looks that the only purpose is to charge cheap, consume from battery while expensive and have a limited benefit from PV.

100% correct. The intention is to charge at night and consume in the day. If I can get the system to also use any spare PV output, so much better.

Just shut off the main breakers and can confirm in its current form it is a UPS. If the mains fails, it will continue to feed back to the grid, so I have shut it down as dangerous.

The reason of powering the grid while “off” is the AC In and AC Out direct connection. Do not use it while connected as in your drawing !

For your intended purpose, the only connection of inverter should be on AC In, through 20A MCB to the mains.

Nothing connected on the AC Out so no “UPS” function.

All consumers are also connected to the mains, at the same point as Multiplus II.

Basically, your Victron MP II, along with battery and grid meter will form a powerwall.

Victron grid meter should be placed in a way to monitor all components: consumers, Multiplus II and existing PV.

Yeah, the in-out connection makes perfect sense as a UPS. But will it deliver inverter power to V In if V Out 1&2 are not connected?, because that would imply V In and V Out are internally connected…

As @nickdb mentioned, it is very advised to learn the system before any planning or building. Please take your time and have a look on as much related documentation as possible.

That will answer to many of your questions and will greatly help in understanding Victron/Multiplus enviroment.

And the answer to your question is yes, AC_In and AC_Out are internally tied during grid connected operation.

Having only AC_In connected and corectly configured, will still supply the consumers, those will be seen as AC Loads.

With the help of Victron grid meter, will be able to compensate all/partial load, depending on PV production and loads.

Thanks, I am also going back and forth with my son, who is a qualified electrician. So If I read this correctly, disconnecting V Out entirely would still allow the inverter to power the house, but allow the LOM detection to shut it down if V In loses the mains?

Yes.
Please do the training.
These are very basic questions covered in all the materials that really should not be asked at this stage of the game.
The forum is not a substitute for training or an experienced Victron installer.
This gear is expensive and getting it wrong can, literally, hurt.

Good luck with the build, Wiggo! The Victron training materials are actually really well put together — worth the time before you start wiring things up.

OK, that was a useful dive into training material, and a closer dig in the db and loft showed the Growatt PV inverter only has a single connection. So the 16A MCB is the Growatt feed in, the 20A is the Victron feed in/out. That leads me to believe that this config will stop the UPS behaviour and allow the MP2 LOM to shut it down in the event of mains loss. Anyway, will check some more later

This diagram is right for your intended way of use.

Though, being an inverter, when grid goes down, will go into island mode and start to invert, so the AC Out_1 will present 230V and a small amount of energy will be consumed from battery.

Of course, AC_In will be disconnected so no danger to that side.

Just for curiosity, why is that you do not use it also as backup system, in case of power down or power glitch ?

Yes, it all seems to be working fine and killing the input shuts everything down, so it is safe. Three reasons for not running it as a UPS: 1) the wiring changes needed to achieve this in an existing and recently renovated and rewired house aren’t worth the benefit, 2) I work from home and if the power is out, chances are local broadband is out, too 3) we lose power here once or twice a year when they do network upgrades. The fridges and freezers are fine for a few hours, and if the heating is out, we have a log burner

The real issue is daytime electricity is 26p+/unit, and overnight tariffs are 6.6p/unit. If I can time shift my usage, I can reduce my bill by 75%