Modbus function 4 is Read Input Registers.
The EVCS contains only Holding Registers.
Please try Modbus function 3 (Read Holding Registers) — it should work.
P.S. I think @Sdb is referring to the GX device. The EVCS does not contain an MQTT broker. This is only possible if you have a GX device in your system. Through the MQTT broker on the GX, you can control the EVCS also.
but there must be some sort of bug in node-red, using a modbus flex getter, I have to injet via a function node, not via the inject node directly(as that causes an error)
Anyway it works.
Is it fc 6 to alter the max charge current value, that’s what I need to work on next.