# No way to configure Grid Code Spain with Victron Multiplus II 48V 5kW GX

**URL:** <https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215>\
**Category:** DIY\
**Tags:** multiplus\_2\_gx, beginner, dess, ess\
**Created:** [14 December 2025 20:42 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215 "2025-12-14T20:42:54Z")\
**Posts on this page:** 15\
**Page:** 2

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:58 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/21 "2025-12-14T21:58:53Z")

</div>

But Grid Meter is set to Inverter/Charger … not the Shelly … or do you use the Shelly for other stuff and not for the Grid Metering ?  
But Inverter/Charger would work … because you have ALL the Loads on AC Out !

But I still don’t understand… Is the ESS working now, or are you getting error messages in the console?

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 22:05 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/22 "2025-12-14T22:05:00Z")

</div>

I use Shelly EM for other purposes, I use it for Home Assistant . It was there before the Multi.  
If I manually Change to inverter it works and if I use the Venus Schedule charger it works. but It doesn’t work to power Assists or to use the Dynamic ESS.

Manually here I can activate Inverter:

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/7/a/7a1b12af1880bdcb4acebc5632fbc4ad975e43fd.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 22:08 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/23 "2025-12-14T22:08:43Z")

</div>

But that’s not what ESS was developed for… ESS always stays connected to the power grid… otherwise it doesn’t make sense.

BUT ESS is working now … or not ?

What is the technical purpose of your system?

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 22:15 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/24 "2025-12-14T22:15:03Z")

</div>

No, it is not working. The system never uses the battery while the grid is connected.  
The only way to make the battery discharge is by completely disconnecting the grid.

This is the actual problem and the reason why I am trying to activate the grid code.  
In _On_ mode, I am not able to use the battery at all.

That is why I initially thought the issue might be related to the grid code configuration.

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [15 December 2025 08:13 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/25 "2025-12-15T08:13:28Z")

</div>

But that has nothing to do with your ESS problem… it has to do with battery usage and a possible misconfiguration…

“As you wrote : Whenever I apply these Grid codes, the unit **fails to accept the grid** and enters a loop (restarts / grid not accepted). As a consequence, **ESS remains in state #3 (“ESS disabled** because no valid grid code / grid not accepted”).”

So… ESS is working… we can see that… …  
Now on to the next problem

Show us your ‘compilation’ of the ESS Assistant… you can display this in the assistant overview… your system does not seem to accept the battery yet…

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [15 December 2025 18:52 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/26 "2025-12-15T18:52:35Z")

</div>

> [@Netrange](#):
>
> Show us your ‘compilation’ of the ESS Assistant

Thank you for following this:  
Do you mean this:

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/0/9/095b161dddfc88e91266be5b99790e9d58ecccc4.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/0/d/0d0d3d9282d1a9fed47e8da5d44b1e677a86f4b8.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/6/9/6984daabd4ab672e97c88328008d16c19f93d43c.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/8/4/84f60a42f57608334265c97804c952e5db1af1cc.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/8/7/874a2a596d1e8ac12ba84ed489964b529487607e.png)

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [15 December 2025 18:55 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/27 "2025-12-15T18:55:56Z")

</div>

![image](https://europe1.discourse-cdn.com/victron/original/3X/b/c/bc2e6f11d2ee4bcf0f047c47ea312a3b0bb3b92c.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [15 December 2025 19:55 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/28 "2025-12-15T19:55:37Z")

</div>

That looks good for now, but you can change all 4 values… since you have a 16S LiFePo battery. … and no AGM etc …

I would be interested to know the values from the GX…  
Akku / Parameters … CCL … CVL … DCL

 ![grafik](https://europe1.discourse-cdn.com/victron/original/3X/c/a/ca51e0e5d4e8583d3bbd9e0b7f4b7999a9d6881d.jpeg)

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [15 December 2025 19:58 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/29 "2025-12-15T19:58:02Z")

</div>

here you have

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/e/a/ea6d67aff6b6165ee332aaeecaeabd9b302299e2.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [16 December 2025 08:19 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/30 "2025-12-16T08:19:13Z")

</div>

That looks good… the BMS is releasing the charge and discharge. 👍

Have you adjusted the voltage values in the “Charger” section to match your battery?

 ![grafik](https://europe1.discourse-cdn.com/victron/original/3X/b/8/b8ead860b228937961f08403ceb3f4da7804386f.png)

Then you should charge the battery to 100% SOC… but to do this, the voltage values from the charger must be correct… see above.

There are situations where the battery is only released for discharge once the system has been charged to 100% SOC.

You can also take a look at teh advasnced Settings … Nothing should be marked here.

 ![grafik](https://europe1.discourse-cdn.com/victron/original/3X/4/6/46025b520c1bace4e0943e5ad9fe2f2b4c38a223.png)

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [16 December 2025 23:32 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/31 "2025-12-16T23:32:06Z")

</div>

Yes, I changed all values as you suggested…

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/5/f/5f1b391044025212d8b25b3184f0e969b0741b63.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/0/e/0ea9b876afca3b8f621ce3cf726703012661282b.png)

Only change I have seen is, due the Dynamic ESS is activated, during lower price period, battery is charged, but never is discharged…  
Also I have check if Switch I or II position, it is of course in I. Even I have changed to II, just in case it came wrongly installed but is ok. Now is again in I.

I’m still thinking my problem is this one, and could be related to Battery configuration as you suggest.

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/7/d/7d1bbf74628766c126118fbd7275ec6f28abd89d.png)

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [16 December 2025 23:51 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/32 "2025-12-16T23:51:05Z")

</div>

Other weird thing I find is system see 2 batteries, but there is only one. Second is Victron itself detected as battery (I don’t know if this is normal or not)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/e/a/ea2bb47cea298b90c32b1a85f71b427030467fd0.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [17 December 2025 07:32 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/33 "2025-12-17T07:32:01Z")

</div>

That’s completely normal… the Multi can also be used as a battery monitor… that’s why it’s important that the battery is selected as the battery monitor… so everything is OK.

You should deactivate DESS and first see if the “normal” ESS control works with the Spanish grid code.  
Since you have selected “NONE” … and therefore no “Spanish grid code,” DESS will not work either.

Whether DESS works the way you imagine it is another matter… there are always problems with the control here… the settings are particularly important for it to work properly…

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [17 December 2025 22:07 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/34 "2025-12-17T22:07:13Z")

</div>

Nothing. DESS is deactivated and battery at 100% and still not getting energy from Battery. During weekend I will start from scratch to discard anything with the software or the installation.

Any suggestion to check in the impedances of AC-In and AC-Out (with all cables disconnected)?

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/d/9/d9988dc69f71c666057c97194105ed7959f5c085.png)

Regards

Finally system was defective and was repared in official support.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [1 March 2026 19:39 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/35 "2026-03-01T19:39:28Z")

</div>

Closed on 1 March 2026 19:39 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.

[Previous page](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215.md?page=1)