# No way to configure Grid Code Spain with Victron Multiplus II 48V 5kW GX

**URL:** <https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215>\
**Category:** DIY\
**Tags:** multiplus\_2\_gx, beginner, dess, ess\
**Created:** [14 December 2025 20:42 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215 "2025-12-14T20:42:54Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 20:42 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/1 "2025-12-14T20:42:54Z")

</div>

I am experiencing an issue with a Victron Multiplus II GX when selecting the grid code “Spain” or “Europe”

Whenever I apply these Grid codes, the unit fails to accept the grid and enters a loop (restarts / grid not accepted). As a consequence, ESS remains in state #3 (“ESS disabled because no valid grid code / grid not accepted”).

The system works normally with None Grid code, but then I lose the option to use the battery energy combined together with the grid energy. or use the Dynamic ESS. I is not activating the Batery to feed my installation. I can only activate the inverter manually.

To rule out external causes, I have tested the unit in a minimal configuration:

- All downstream AC loads disconnected

- Only AC-IN connected (L + N)

- Protective Earth (PE) correctly connected to the Multiplus PE terminal and bonded to chassis

- No external Neutral–Earth bond present anywhere

Any idea’?

Thanks in advance

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 20:50 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/2 "2025-12-14T20:50:10Z")

</div>

**“bonded to chassis”** … sounds like a motorhome installation …

How is the multi connected? Are L and N the right way round?

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 20:56 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/3 "2025-12-14T20:56:27Z")

</div>

😉 Sorry.. I meant: Protective Earth (PE) is connected to the Multiplus PE terminal and to the metal chassis, which is connected to the building grounding system.  
Yes, they (L & N) are right, I have double checked and checked with the Multimeter.

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:03 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/4 "2025-12-14T21:03:35Z")

</div>

No problem… 🙂  
What are the voltage values from the mains?  
Do you have a picture of the GX display… You can easily attach pictures here…  
Try the German network code…

If the multi has already worked… the connection MUST be correct… sorry for asking…

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:09 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/5 "2025-12-14T21:09:12Z")

</div>

Thank you for your help:

I also tried the German Grid Code with the same result. I’m thinking in restore to factory settings and start from scratch.

Here you have an screenshot with the voltages

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/0/1/011f9a022304036954c5822a02b586cb2e7d3757.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:10 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/6 "2025-12-14T21:10:13Z")

</div>

Are you configuring with the MK3 …or via VRM?

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:13 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/7 "2025-12-14T21:13:09Z")

</div>

I’m using the MK3

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:15 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/8 "2025-12-14T21:15:46Z")

</div>

… perfekt …

 ![grafik](https://europe1.discourse-cdn.com/victron/original/3X/4/b/4beddf872188c7cb334e1b466c91902597f14366.png)

this would be interesting …

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:24 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/9 "2025-12-14T21:24:53Z")

</div>

here you have:

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/8/1/813db7f056f50bfd394c8857c59fe38d6fe40712.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:26 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/10 "2025-12-14T21:26:55Z")

</div>

looking goood 👍

Then show us the settings from your ESS assistant.

 ![grafik](https://europe1.discourse-cdn.com/victron/original/3X/f/1/f19bbc685bbc5a00786869544b7e773671563924.png)

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:32 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/11 "2025-12-14T21:32:15Z")

</div>

do you mean this?

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/8/b/8b60edc45ec8272921a7e2eb33ea654f2a130ec7.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:32 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/12 "2025-12-14T21:32:40Z")

</div>

Yes … 👍 … configured ?

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:34 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/13 "2025-12-14T21:34:15Z")

</div>

To be able to activate the ESS Assistant, I changed to Spain Grid code, then removed the Spain Grid Code and let the other options.

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:36 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/14 "2025-12-14T21:36:40Z")

</div>

![image](https://europe1.discourse-cdn.com/victron/original/3X/8/7/872cb771da0b92663aa877c2dbf5c8901f312236.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/3/b/3b64a65270f679002f1be65db4ec2b3fa2259333.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:39 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/15 "2025-12-14T21:39:30Z")

</div>

Looks good… 👍

What kind of battery are you using?

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:42 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/16 "2025-12-14T21:42:10Z")

</div>

ECO-Worthy 48V/5Kw connected with CAN

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/1/3/137d8928c1565f1ebcd45db03e4359839120385f.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:47 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/17 "2025-12-14T21:47:05Z")

</div>

Then you don’t need the “optimized with battery life” mode… you can set it to… without battery life… since it’s not a lead battery…  
But you have a single-phase power supply in Spain, right?

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:48 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/18 "2025-12-14T21:48:35Z")

</div>

yes, we have single phase power

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 December 2025 21:50 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/19 "2025-12-14T21:50:39Z")

</div>

you could set this to “single phase”

 ![grafik](https://europe1.discourse-cdn.com/victron/original/3X/2/2/222723e77e5e96ab8097787481d3ba62c0c89aa2.png)

Did you have “ESS Errors” yet …

and have you all your Loads AFTER the Multi ?

---

<div class="post-metadata">

**Author:** ![ChamboCT](https://avatars.discourse-cdn.com/v4/letter/c/7ba0ec/32.png) [@ChamboCT](https://community.victronenergy.com/u/ChamboCT)\
**Post date:** [14 December 2025 21:55 UTC](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215/20 "2025-12-14T21:55:14Z")

</div>

ok, I change it.  
Not yet. I get one in VE.Config when I change from Spain code to None code. related to ESS. just that.  
Yes, I have all loads in AC-OUT1. AC-OUT2 is empty. Only thing before Multi is a Shelly EM meter.

[Next page](https://community.victronenergy.com/t/no-way-to-configure-grid-code-spain-with-victron-multiplus-ii-48v-5kw-gx/50215.md?page=2)