Issue: Turning on Multiplus ii, Inverter on, voltage only 270 mV measured at AC out 1 terminals. Battery voltage at 13.8 V and measuring fine at inverter connections.

Please help! There are such limited resources online about this.

I am testing a newly installed Multiplus ii - I have two SOK 315 A batteries in parallel that have been working fine with the DC system. I turn the inverter on in Inverter mode, no blown fuses, 13.8 V at inverter connections from batteries, ground is connected, and AC OUT 1 is measuring only 270 mV directly pushing the multimeter into the connector hot and neutral. I see this same voltage at distribution panel and outlets.

I followed battery manual and instructions for configuring the inverter correctly, so I don’t think there is a problem there.

Any ideas?

---

<div class="post-metadata">

**Author:** ![MikeD](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/miked/32/1522_2.png) [@MikeD](https://community.victronenergy.com/u/MikeD)\
**Post date:** [21 April 2026 02:39 UTC](https://community.victronenergy.com/t/newly-installed-multiplus-ii-output-1-low-voltage/56819/2 "2026-04-21T02:39:19Z")

</div>

Which model multiplus?  
If it has an internal fuse, then check that. Try with no wiring connected to any AC port. If you configured the unit you have a Mk3 adapter, so try resetting to factory defaults, just in case you have something strange in your config.