Since a week i have 4 parallel lifepo4 batteries, 300a per unit. They are 16 cell, Chinese (delongtop) with their own BMS, connected to Cerbo.
I put it in charger only mode and it immediately charged from 55% to 99 and now it has been pushing the voltage from 53.5 to 57.2, taking 4 days already and only taking 1A in this phase.
Ma manufacturer specifies absorption voltage 57.6 and float 53.5-54.5 with 20 minutes absorption time.
I am going to use the batteries in a DESS setup, connected to the grid. Charging in cheap hours and using the battery in expensive hours.
So if I am correct: it needs to top balance every 1 or 2 weeks. Will that mean that every time it does, it takes 4 or 5 days to reach 100% charge /57.6v ? And that I cant use the battery as intended in the meanwhile?
There are many variables that affect this.
- What are the charger settings supplying charge to the batteries.
- How good is the quality of the cells / bms.
- Is the bms set up correctly.
- Is the bms capable of balancing to a suitable amount.
- Do the cells keep within acceptable limit, with normal use.
- Does normal use allow charge voltage to get to higher enough voltage to balance.
- If yes to 5+6, is a scheduled balance charge required.
- What you consider is an aceptable deviation in cell voltages.
- How often you want to top balance.
@ferdyvw
Most (many) life4po battery owners never reach 100%, check topics here, and it doesn’t matter.. 99% is even better for the battery then always want 100 % and have risk of cell over-voltage.
Cell balancing is only required above 50 mv cell voltage difference at +99 % SOC.
Thanks Frisianstar,
So knowing that the BMS limits current very much when reaching 99,% and 53,5v, it takes a long time to reach set absorption voltage 57,6%; what absorption and float voltage would you recommend? I am completely new in this and need some general direction to start while learning.
55.2 Volts is my absorbtion limit and also the 100% SOC value..most of the it hangs on 99% that’s ok for me.. I don’t like overcharged batteries anyway.
At 57.6volts the overvoltage protection kicks in! 16 cell battery, should be lower like 56.5 Volts.