Hi Everyone,
A few days ago we had a power cut, and so the house with the solar micro inverters on the output had still power because of the UPS function.
3x Multi RS off-grid: DESS holds battery charge rate at 0 W, system frequency-shifts the AC-coupled PV off for 2 hours.
SYSTEM
- 3x Multi RS Smart 48V/6000VA/100A, one per phase (L1/L2/L3), firmware v1.31
- Cerbo GX MK2, Venus OS v3.79
- Enphase microinverters on AC-out, read in as a SunSpec PV inverter, 6.48 kW total devided over 3 phases.
- Grid meter: Energy Meter VM-3P75CT
- Battery: 840 Ah bank, JK-BMS over CAN. Active battery service = SmartShunt 500A
- Dynamic ESS (DESS) active, ESS minimum SoC 15%, AC input current limit 25 A
- Multiphase regulation: “Total of phases”
All figures below are VRM logged data at 1-minute resolution.
WHAT HAPPENED
The street lost power at 11:01. The Multi RS units kept the house alive without
interruption - that part worked perfectly. But the Enphase microinverters produced
almost nothing for the next 2 hours 12 minutes, because the system kept shifting the
output frequency to 52.7 Hz.
11:01 Grid lost. Active input goes to “not connected”. Enphase was making 1375 W
11:02 Output voltage 240 → 229 V. Output frequency jumps to 52.7 Hz. Enphase drops to 17 W
11:04 “Grid lost” alarm
11:02 - 13:12 Frequency cycles between 50.0/50.1 Hz and 52.7 Hz (peaks to 53.3 Hz)
roughly every 2-3 minutes. 56 of those 131 minutes are at or above 52.0 Hz
13:15 DESS releases its charge restriction. Frequency returns to 50.0 Hz and stays
there. Enphase ramps to 3-5 kW - while still off-grid
14:00 Grid returns
PV energy produced during the 2 h 12 min of frequency cycling: 0.10 kWh.
PV energy produced in the 33 minutes right after 13:15, still off-grid: 1.71 kWh.
WHY I THINK DESS IS THE CAUSE
Throughout the whole outage, DESS commanded a battery charge rate of 0 W (logged in
VRM as “DESS Charge Rate”). It had been 0 W since before the outage started.
So the system was in this state:
- No grid
- House load only 100-400 W
- Battery at 18.9% SoC, BMS charge current limit 360 A, charge voltage limit 55.2 V,
battery voltage 51.7 V - plenty of room - DESS saying: charge rate 0 W
- Enphase wanting to deliver 1.4 kW
With nowhere to put the power, frequency shifting is the only lever the Multi RS units
have left. The battery was actually discharging at 1-12 A for the entire off-grid
period, and SoC fell from 18.9% to 17.9%.
The moment DESS changed its mind at 13:15, everything snapped back to normal - with no
change on the grid side:
- DESS Charge Rate: 0 → 5137 W, ramping to 16600 W by 13:27
- DESS Restrictions: 3 → 0
- DESS Strategy: 3 → 2
- Battery current: -4 A → +7 A in the same minute, +55 A three minutes later
- Output frequency: flat 50.0 Hz from that minute on
- Enphase: 2 W → 526 W → 3-5 kW
The grid did not come back until 14:00, so for 45 minutes the system ran off-grid with
the Enphase at full output and a rock-steady 50.0 Hz. That is the control experiment:
same off-grid conditions, only the DESS charge restriction removed.
WHAT I RULED OUT
- No alarms or faults on any of the three RS units for the whole period: error code 0,
mode “On”, no overload, no DC ripple, no high/low DC or AC voltage alarm, no short
circuit, no “sustain” active, no “energy meter missing”. State stayed 252 “Ext.
control” throughout. - No PV inverter power limit was set. The Power Limit attribute was 0 / not in use all
day; my own limiting setup only went live two days later. - Battery was not full and could accept charge - proven by the +55 to +88 A it took as
soon as DESS allowed it. - Not a “battery can’t keep up” situation - load was 100-400 W against 1.4 kW of PV.
WHY THE ENPHASE NEVER RECOVERED ON ITS OWN
52.7 Hz is above the over-frequency trip point of the Enphase grid profile (~52.0 Hz
for EN 50549-1 OF2). So instead of derating on a frequency-watt curve, the
microinverters trip off completely and start their reconnect timer. The ~2-3 minute
cycle in the data matches that reconnect delay: they come back, ramp up, the RS units
immediately shift to 52.7 Hz again, and they trip out. Repeat for two hours.
MY QUESTIONS
- Is this expected behaviour? Should DESS’s charge rate command still be enforced when
the grid is lost and the system is islanded? I would expect DESS to stand down and
let the system run as a plain ESS/off-grid system. - If it is expected, is there a setting to make DESS release its restrictions on grid
loss - or does this have to be handled externally (I run Node-RED and can force it)? - Is the frequency shift range configurable on the Multi RS? Jumping straight to
52.7 Hz hard-trips any PV inverter whose profile trips at 52.0 Hz. A range ending
around 51.0-51.5 Hz would derate the Enphase instead of knocking it out. - Has anyone else seen 3x Multi RS + AC-coupled PV on AC-out + DESS behave like this
during an outage?
Raw 1-minute CSV of the event is attached if anyone wants to check the numbers.
BTW the energy prices were positive all day long.