# MultiPlus2 stops discharging. SoC never comes down to 10%

**URL:** <https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963>\
**Category:** DIY\
**Tags:** victron\_community, bms, multiplus-ii, ess, multiplus\
**Created:** [24 September 2024 15:40 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963 "2024-09-24T15:40:38Z")\
**Posts on this page:** 15\
**Page:** 1

<div class="post-metadata">

**Author:** ![Alois](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alois/32/47594_2.png) [@Alois](https://community.victronenergy.com/u/Alois)\
**Post date:** [24 September 2024 15:40 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/1 "2024-09-24T15:40:39Z")

</div>

Seeing MuliPlus-II warnings “Low battery voltage” evn the BMS shows cell voltage fare away from warning or alarm level.  
When the warning chage to alarm status the ESS (I think) stops discharging and change to grid supply. This happens when SoC is in a range of 20-30%.  
SoC is set to 10% in the ESS.

Edition: ESS mode is “Optimiert (ohne BatteryLive)” \> “Optimized (without BatteryLife)”

---

<div class="post-metadata">

**Author:** ![dognose](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dognose/32/968_2.png) [@dognose](https://community.victronenergy.com/u/dognose)\
**Post date:** [24 September 2024 15:57 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/2 "2024-09-24T15:57:40Z")

</div>

Are you Ecentually running in “Self Consumption with Battery Health” mode?

Then the mininum soc will be increased based on days, where you don’t reach 100%.

So, the system then can use ranges from 100 to 60, rather than 50 to 10 all day.

Everytime you reach 100%, the effective soc limit will be lowered again.

---

<div class="post-metadata">

**Author:** ![Alois](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alois/32/47594_2.png) [@Alois](https://community.victronenergy.com/u/Alois)\
**Post date:** [24 September 2024 17:05 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/3 "2024-09-24T17:05:33Z")

</div>

ESS mode is “Optimiert (ohne BatteryLive)” \> “Optimized (without BatteryLife)”

Thanks for feedback!

---

<div class="post-metadata">

**Author:** ![Alois](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alois/32/47594_2.png) [@Alois](https://community.victronenergy.com/u/Alois)\
**Post date:** [24 September 2024 17:06 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/4 "2024-09-24T17:06:27Z")

</div>

ESS mode is “Optimiert (ohne BatteryLive)” \> “Optimized (without BatteryLife)”  
Thanks for feedback!

---

<div class="post-metadata">

**Author:** ![BjoernK](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/bjoernk/32/89_2.png) [@BjoernK](https://community.victronenergy.com/u/BjoernK)\
**Post date:** [24 September 2024 17:07 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/5 "2024-09-24T17:07:12Z")

</div>

@Alois  
Check in MP2 VeConfigure of you activated Dynamic SOC and/or Battery Monitor.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [24 September 2024 17:33 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/6 "2024-09-24T17:33:35Z")

</div>

It is likely the [dynamic cut](https://www.victronenergy.com/media/pg/Energy_Storage_System/en/controlling-depth-of-discharge.html#UUID-b628c51f-379e-c806-6073-cacbc9fc3fdd) off in the ESS assistant.

Check your voltage drop from your battery terminals to the dc terminal on the inverter.

---

<div class="post-metadata">

**Author:** ![Alois](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alois/32/47594_2.png) [@Alois](https://community.victronenergy.com/u/Alois)\
**Post date:** [25 September 2024 12:27 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/7 "2024-09-25T12:27:24Z")

</div>

There is a Lynx Shunt between the battery connetor and the distributor box. However I could not measure any voltage drop across the shunt. I wounder because a shunt is a resistor and the voltage across it is the measured parameter ??

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [25 September 2024 19:57 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/8 "2024-09-25T19:57:15Z")

</div>

Measure voltage at the inverter terminals, then measure it at the battery terminals - compare?  
The shunt drop is for its own measurements.  
Make sure you have correctly torqued and crimped all connections.  
The other way to do it is to use the DMM on AC and measure voltage from pos to pos or neg to neg (one probe on battery terminal and one on the inverter terminal) and check voltage.  
Its important to A. Be careful and B. Do so underload.  
A third way is to use ve config and check DC ripple (under load)

---

<div class="post-metadata">

**Author:** ![Alois](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alois/32/47594_2.png) [@Alois](https://community.victronenergy.com/u/Alois)\
**Post date:** [4 October 2024 11:10 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/9 "2024-10-04T11:10:18Z")

</div>

Status:

- SoC 43% Load ~8kW  
Battery: 49.5V MP2: 49.0V  
Load ~12kW \>\> Low bat alarm \>\> switch to grid \>\> Battery goes to more than 50V  
In any case DC cell voltage is more than 3V; no alarm from BMS all time
- All connections are perfect!
- Measure DC ripple to be done soon. Question: DC ripple is shown in ve config?

---

<div class="post-metadata">

**Author:** ![Alois](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alois/32/47594_2.png) [@Alois](https://community.victronenergy.com/u/Alois)\
**Post date:** [4 October 2024 11:23 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/10 "2024-10-04T11:23:30Z")

</div>

Just checked:  
Load SoC 53% Load ~8kW  
AC voltage (+bat to +MP2) 0.04V  
Low Bat starts blinking at the MP2. Stop blinking when I reduce the load to 4kW.

---

<div class="post-metadata">

**Author:** ![M\_Lange](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/m_lange/32/16_2.png) [@M\_Lange](https://community.victronenergy.com/u/M_Lange)\
**Post date:** [4 October 2024 11:40 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/11 "2024-10-04T11:40:30Z")

</div>

What battery do you have?  
Add your VE.config file or make some screenshots of your settings.

---

<div class="post-metadata">

**Author:** ![Alois](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alois/32/47594_2.png) [@Alois](https://community.victronenergy.com/u/Alois)\
**Post date:** [7 October 2024 14:31 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/12 "2024-10-07T14:31:44Z")

</div>

Hi Matthias

 ![241007 Victron](https://europe1.discourse-cdn.com/victron/original/2X/2/21b284da18fedcf467049da8f7437675632fb59b.png)

Batt-Voltage is min ~49V DC (16cells). Ripple is 400mVpp at the MP2 terminal (load. 8kW).  
Measurment was done by a battery powered Oszi.

Attached the ESS battery setting. Does “Optimiert” mean the alarm limits are calculated? In other words … when I put the min SoC to 10% in the settings this has no meaning?

---

<div class="post-metadata">

**Author:** ![Alois](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alois/32/47594_2.png) [@Alois](https://community.victronenergy.com/u/Alois)\
**Post date:** [3 November 2024 15:54 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/13 "2024-11-03T15:54:34Z")

</div>

Problem solved meanwhile

 ![Screenshot 2024-11-03 165125](https://europe1.discourse-cdn.com/victron/original/2X/7/70ffdfc6de4a226eb6af26ad1a9c1ed4ad9a18ec.png)  
Limits in th Assistant for dyn switch off have been too high: 52V.  
Setting all to 46V works great!  
Thanks to all for help!

---

<div class="post-metadata">

**Author:** ![grfloater](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/grfloater/32/3636_2.png) [@grfloater](https://community.victronenergy.com/u/grfloater)\
**Post date:** [7 November 2024 20:03 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/14 "2024-11-07T20:03:02Z")

</div>

Thank you for the tip.  
Same here, with SOC limit set to 10% (and active ~10-15%), I had shutdowns at ~28%.  
Setting for 0.005C was at51.5V, while battery was going \<50.50V at SOC \<20%.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [21 November 2024 20:03 UTC](https://community.victronenergy.com/t/multiplus2-stops-discharging-soc-never-comes-down-to-10/4963/15 "2024-11-21T20:03:36Z")

</div>

Closed on 21 November 2024 20:03 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.