Multiplus showing absorption light but low amperage

Has anyone some thoughts? I have just set up a Multiplus ii, updated all firmware, plugged into a Lynx smart bms connected to 4 x 12v180ah lithium batteries in parrallel. All looks good, batteries are balanced, amperage is around 0.2amps and GX is showing ext control. However, the Multiplus never moves off the Absorption light to Float and cannot figure out why. I havent put any loads on the system yet. Concerend I’ve got a setting wrong somewhere.

Pls post Screenshots of the settings

The multiplus is now under external control by the Lynx BMS, it is not running its own charger algorithm so it does not have its own bulk, absorption & float stages so it always shows absorption to indicate it is charging.

Ok, many thanks, did wonder. Would be an elegant solution if Multiplus could mirror the Lynx so dont have conflicting indicators. Having said that very impressed by the whole setup.