No shore power connected: everything works fine, both 24V and 230V.
Shore power connected and the Multiplus in charging mode: everything works fine, both 24V and 230V.
Shore power connected and the Multiplus in inverter mode: 230V works fine, but occasionally the 24V briefly drops out, and I believe an overload is sometimes reported as well.
Check the battery connections and/or those of the MP (terminals clean, cable lugs crimped correctly, tightened to the specified torque); if necessary, inspect them using thermography.
Were the correct cable cross-sections used? Was the required number of cables used (for MPs with two or more connections per pole)?
Use quality high-current fuses, not cheap automatic circuit breakers with a high voltage drop (which tends to change under thermal load).
The larger Mp units are generally wired with two conductors per pole (the 3 kVA unit has one screw, while the higher power classes have several to reduce the contact resistance and keep the cables manageable), because a single 140 mm² cable is not as easy to route as two 70 mm² cables.