# Multiplus not starting in BULK

**URL:** <https://community.victronenergy.com/t/multiplus-not-starting-in-bulk/16718>\
**Category:** Q&A and troubleshooting\
**Tags:** battery\_charging, offgrid, multiplus\
**Created:** [27 December 2024 17:03 UTC](https://community.victronenergy.com/t/multiplus-not-starting-in-bulk/16718 "2024-12-27T17:03:19Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![dirk](https://avatars.discourse-cdn.com/v4/letter/d/87869e/32.png) [@dirk](https://community.victronenergy.com/u/dirk)\
**Post date:** [27 December 2024 17:03 UTC](https://community.victronenergy.com/t/multiplus-not-starting-in-bulk/16718/1 "2024-12-27T17:03:19Z")

</div>

For over 7 years my MultiPlus 24/5000 was working perfect.  
Over last summer I updated it from (if I remember right ) 3.xx through 4.xx to 522  
Now, when I turn on the generator it starts either in Absorption or Float although the SOC is low enough.  
I see I’m not the only one, reading the topics here and on the web.  
Someone posted a workaround by shuttng the MP off and on again.  
This works, it will start in Bulk and reacts as it used to.  
However this is very unconveniant as the power has to be shut off every time I want to charge by generator…

The configuration of the MP hasn’t changed and as it is working properly after turning on the MP I don’t think this is the problem.

As I see it, this problem is caused by the “new” firmware (correct me if I’m wrong)  
If this is true, was this bug also present in 4.xx?  
Can I downgrade to firmware 4.xx or even 3.xx?

Or more preferably (as I already monitor all my devices by modbus); is there a write by Modbus protocol that forces the MP to go into Bulk state?

(or perhaps will there be a new firmware that tackles this problem any time soon?)

 ![Scherm­afbeelding 2024-12-27 om 16.51.53](https://europe1.discourse-cdn.com/victron/original/2X/d/d8482bcd41c9af9ece8bd2d9834cfe2ac44a0336.png)

Thanks  
Dirk

VenusGX  
BMV 702  
BlueSolar MPPT 150/85 (VE.Can) 2x  
MultiPlus 24/5000/100/120 2x (second to be connected any time now…)  
Phoenix 24/3000  
Panels 10kW (on 2 solar trackers)  
Battery OPzS 54kWh  
Orion 24/12/70

---

<div class="post-metadata">

**Author:** ![JohnC](https://avatars.discourse-cdn.com/v4/letter/j/9de0a6/32.png) [@JohnC](https://community.victronenergy.com/u/JohnC)\
**Post date:** [28 December 2024 04:59 UTC](https://community.victronenergy.com/t/multiplus-not-starting-in-bulk/16718/2 "2024-12-28T04:59:06Z")

</div>

Hi @dirk  
Try resetting your ‘Repeated Absorption Interval’ to (say) **0.5** days. Then it should reattempt a fresh charge cycle when you start your genset the next day. (Like when you reset the Multi).

If there has been an effect from a firmware change, it may be to better reflect what those settings actually mean, and report it so. Like it may be attempting to finish the cycle it commenced days ago, when your desire may be always to commence a freshy whenever the genset runs.

---

<div class="post-metadata">

**Author:** ![dirk](https://avatars.discourse-cdn.com/v4/letter/d/87869e/32.png) [@dirk](https://community.victronenergy.com/u/dirk)\
**Post date:** [28 December 2024 11:29 UTC](https://community.victronenergy.com/t/multiplus-not-starting-in-bulk/16718/3 "2024-12-28T11:29:15Z")

</div>

Thanks a lot,

Makes sense…  
Changed the configuration.  
Will test and start the genset tomorrow as the batteries are already pretty full by solar right now…

I’ll let you know…

---

<div class="post-metadata">

**Author:** ![dirk](https://avatars.discourse-cdn.com/v4/letter/d/87869e/32.png) [@dirk](https://community.victronenergy.com/u/dirk)\
**Post date:** [30 December 2024 08:41 UTC](https://community.victronenergy.com/t/multiplus-not-starting-in-bulk/16718/4 "2024-12-30T08:41:11Z")

</div>

Yes, this did the trick!  
Again, thank you very much!!!

---