Auxiliary single-phase MultiPlus on a three-phase grid

I have a 12 kVA three-phase grid connection. I’d like to connect a MultiPlus-II 48/5000/70-50 to one phase for backup power and peak shaving. It will be about ten metres away, with a cable running to the Enedis connection. I’d also like to add a main switch and surge protection just before the AC input at this point. I plan to run two neutral cables to the consumers for the phase downstream of the MultiPlus and the two other phases.
I have a few questions about this setup:

  • Is it better to protect the AC input with a 20 A circuit breaker? The cable is already fused at 20 A by Enedis. I’d like to set the AC input current limit in the software to a moderate 20 A.
  • I’d also like to add solar panels via a three-phase inverter so that it can flexibly supply each phase wherever power is needed. I think I’ll connect it to the AC output. I know the three-phase inverter won’t work during a grid outage, as the other two phases won’t have backup power. The cables to the consumers can handle 40 A. Should I add a 40 A circuit breaker? I’ve set the AC output current limit in the software to a moderate 40 A. How can I make sure the MultiPlus-II and the inverter can’t supply more than 40 A? Or should I connect the inverter to the AC input?
  • I often see 2-pole circuit breakers. What are their advantages over 1P+N circuit breakers?

Regarding the last point, two-pole circuit breakers are polarity-independent on the AC side (in RV applications when you can’t know the wiring configuration of the shore power connection, as well as in PV technology).