I’m looking to install a MultiPlus-II 48/3000/35 (GX) + 2.5 kWh LFP battery at home in New Zealand for use purely as an unattended “UPS” for a critical mains-powered stormwater pump. Obviously I’ll get an electrician to wire it up to the mains but I’m going to do as much of the engineering myself as I can to avoid surprises.
There is no solar setup and I just have a simple domestic 230V 60 A 1-ph service. The pump is on a 20 A circuit and currently has a diesel generator + ATS inline as a backup. The problem with a generator solution however is the number of starts required during a heavy rain event can deplete the 12V starter battery.
Power failures during rain are rare, perhaps happening only once every 5-10 years but I have to cover the possibility to avoid property damage.
The in-tank pump draws 1.25 kW over the 1 minute it typically runs when triggered, that being when the tank has filled, every 3 mm of rainfall.
The start-up current is measured at 23A (@ 230VAC) for 250mS.
In terms of energy I need about 2 kWh to cover 200mm of rain with a depth of discharge of 70-80%. 200 mm would be a significant rain event but I may be able to retain the generator + ATS upstream of the MultiPlus and trigger that if needed.
Questions:
-
I would like to use a 48VDC system (instead of 24V) but I see there is a Victron ‘recommendation’ for 100 Ah minimum battery size?
I’d like to use a 52 Ah. Is there any technical basis behind that recommendation? -
The MultiPlus and battery need to be outside on my patio but will be under cover next to the generator. I anticipate installing both in a standard electrical enclosure (with vents added) but one large enough is hard to find when taking into account the recommended 100mm clearance around the MultiPlus. If I use two enclosures how do I run the battery wires between them without using a ‘closed conduit’ as the install manual says not to do?
Thanks for any comments or suggestions.