# MultiPlus II 4k5 doesn't seem to follow my grid setpoint in ESS

**URL:** <https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566>\
**Category:** DIY\
**Tags:** multiplus-ii, diy\
**Created:** [5 October 2026 18:26 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566 "2026-10-05T18:26:46Z")\
**Posts on this page:** 17\
**Page:** 1

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 18:26 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/1 "2026-10-05T18:26:46Z")

</div>

MultiPlus-II 4k5 doesn’t seem to be following my grid setpoint in ESS

Whatever value I set, the AC input goes straight through to AC out

---

<div class="post-metadata">

**Author:** ![M\_Lange](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/m_lange/32/16_2.png) [@M\_Lange](https://community.victronenergy.com/u/M_Lange)\
**Post date:** [5 October 2026 18:34 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/2 "2026-10-05T18:34:10Z")

</div>

Could you please add some more information about your system and maybe a screenshot?

---

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 18:39 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/3 "2026-10-05T18:39:45Z")

</div>

what settings do you want to see ?

It is a standard installation multiplus II 4k5 AC in to grid, AC out 1 to my own home. No energie meter but that shouldn’t be a problem I think since all ac loads are at AC out 1 and with the following settings

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/b/f/bf2c3b94a651bd9d01cbda86cac535c9c8855357.png)

I have another multiplus II 5000 and that on works for years. Settings look all the same

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [5 October 2026 18:46 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/4 "2026-10-05T18:46:22Z")

</div>

There are a lot more settings than that screen. What is the inverter configuration? Detail the components, wiring etc.  
At the moment it is guesswork.  
The quality of an answer is determined by the quality of the question.

---

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 18:51 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/5 "2026-10-05T18:51:06Z")

</div>

I understand but there are so manu sub menu’s. What settings should I paste ?

![image](https://europe1.discourse-cdn.com/victron/original/3X/1/8/188c59d9f8b346ab068eade65a693f9c33209b0c.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/b/f/bf95b5ddbdb012870acf0ea696ba1e24b95360a6.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/8/a/8a32a35cb6ba8f6d460124662de736e10468bb3d.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/4/8/485ebc1e6832048a75a7f179e78501060523730d.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/6/9/6921428f70d77cec9d06388d398291b6db8803cd.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/2/5/25de51841efc20716e58d36e7db612ebb46dd734.png)

A difference with my other multiplus is the external current clamp but that is because there are ac loads in front of the multi what is not the case for this multi

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [5 October 2026 18:51 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/6 "2026-10-05T18:51:58Z")

</div>

Start with the inverter configuration file and how the system is built.

---

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 18:54 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/7 "2026-10-05T18:54:06Z")

</div>

This is te ve config ESS configuration

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/a/c/acc397edf8e9a62243ce8c650ccead04128e12a3.png)

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [5 October 2026 18:56 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/8 "2026-10-05T18:56:36Z")

</div>

What battery do you have? Is it visible in dvcc and selected as the managing battery? The battery monitor is the multiplus. This should be a managed battery, or if an unmanaged battery, you should use a shunt as the multiplus is inaccurate with internal dc measurements.

---

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 19:00 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/9 "2026-10-05T19:00:08Z")

</div>

![image](https://europe1.discourse-cdn.com/victron/original/3X/a/e/ae2b1762c6258acb4ebf4c7cdeb648aa78ca3e5f.png)  
 ![image](https://europe1.discourse-cdn.com/victron/original/3X/3/0/30bf815ebf75827131232802f0d9d9c0ef9480ff.png)

There is no BMS connected but that is the same with my other multiplus. My other installation does have two shunts available.  
In this config I don’t have them yet. The connection to the batteries is instable so removed them from this installation.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [5 October 2026 19:03 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/10 "2026-10-05T19:03:38Z")

</div>

The charge voltage setting only applies to a bms, no value choosing this with an unmanaged battery.  
What do you mean by unstable connection?  
ESS relies on a reliable soc, without a shunt that won’t be the case.  
You need to post console screenshots showing the issue you are seeing. It really is unclear, but if you have an unstable system with an inaccurate soc ess won’t work. Best to fix all the challenges first.

---

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 19:08 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/11 "2026-10-05T19:08:37Z")

</div>

I removed the connection to the battery since it disconnects all the time. WIthout this battery connected all notifications are gone so multiplus should be in control

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/c/6/c6e470e83e8e12e67d2e7dded576c13f8ba69301.png)

Just changed the battery monitor to

![image](https://europe1.discourse-cdn.com/victron/original/3X/e/b/eb2991d3b868ff88f143a0090c18d7f354e81e75.png)

but since there is only one device is expect that automatic would be the same

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [5 October 2026 19:11 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/12 "2026-10-05T19:11:18Z")

</div>

I suggest you get a professional to help you, there seems to be an underlying issue with the installation. If you lack a stable foundation, the battery is critical, then problems will follow. This isn’t something we can troubleshoot over the internet.

---

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 19:15 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/13 "2026-10-05T19:15:16Z")

</div>

The current setup should be stable since there is only the multiplus. No other devices, no notifications so looks like a setting I missed.

---

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 19:20 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/14 "2026-10-05T19:20:51Z")

</div>

Hmm, it looks that changing the battery monitor from automatic to the multiplus did the trick but it took a while before it started acting on the grid set point.

![image](https://europe1.discourse-cdn.com/victron/original/3X/d/5/d5ea51d13e89199489f95ba4ab095075d008df9c.png)

---

<div class="post-metadata">

**Author:** ![rns](https://avatars.discourse-cdn.com/v4/letter/r/c89c15/32.png) [@rns](https://community.victronenergy.com/u/rns)\
**Post date:** [5 October 2026 19:32 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/15 "2026-10-05T19:32:12Z")

</div>

Hi Nick,

Thanks a lot. Sorry for the confusion but you kept me searching and finally it started working. Learned that I need some patience when I change values.

WIth my other multiplus I’m used it starts acting immediatly when changing the grid set point but here it looks like change the battery monitor takes some time before the multiplus starts acting on it.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [6 October 2026 05:35 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/16 "2026-10-06T05:35:34Z")

</div>

Always a good idea to set the monitor manually, if there was a change in the system, I have seen it get stuck on an incorrect setting. Easy fix fortunately 🙂

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [20 October 2026 05:35 UTC](https://community.victronenergy.com/t/multiplus-ii-4k5-lijkt-niet-naar-mijn-grid-set-point-te-luisteren-in-ess/63566/17 "2026-10-20T05:35:49Z")

</div>

Closed on 20 October 2026 05:35 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.